We have a relay that is being activated by an induced voltage (115V) in a long cable application.
The circuit is like this: 230V AC 50Hz source, connected to a long 2G1,5 (1,5 square milimiters) cable (400 meters) connected then to an auxiliary contact, then back to the A1 of the relay, then the relay A2 is connected to neutral. In the installation, the cable is separated from power cables a minimum of 15 centimeters.
When we disconnect from its 230V source, the voltage dissappears.
Then we connect again, but disconnect in the auxiliary contact, well-separating the cables, and the voltage is induced in the same way.
Any hint??

Thanks,
Martin

RE: Long cable induction???

Induced voltage can be a problem on long runs. It will go away if DC is used for control voltage.
Steve

RE: Long cable induction???

A trick that I have used several times in the past on long runs is to place a resistor or capacitor to ground or to the chassis to bleed off the induced voltage.  You need to pick a value of sufficient rating to not interfer with the normal operation of your circuit and to withstand when full power is applied.  You will probably find that the induced voltage will collapse with even a small capacitor or large valued resistor.



 

RE: Long cable induction???

(OP)
Thanks to all... yes I placed another relay in parallel just to get away of the problem, just to figure out a solution later. I'll make some resistor in parallel more or less equal to the impedance of the relay. These are not so good... 230Vac relay activates at 114V... damn!

RE: Long cable induction???

Go figger! Half the time I'm wishing a relay would pull in at half its nominal.. And in your case it does and you don't want it to.
 banghead      

Keith Cress
kcress - http://www.flaminsystems.com

RE: Long cable induction???

Perhaps such relays should have a little sensitivity adjustment screw.

 

RE: Long cable induction???

(OP)
Keith
Go buy Omron's :)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources