ASCE 7-05 Increasing Factors (overstrength, redundancy)
I have been going through the ASCE 7-05 as I am starting to get into higher seismic areas. I think I have a grasp as to when the redundancy factor would be greater than 1.0 however I am somewhat confused as to when the overstrangth factor comes into play. I know that you would apply the overstrength factor to say a collector or that you would apply a 1.4 increase for elements of the wall anchorage system per 12.11.2.2.2, however Im unsure as to when else I would apply the overstrength factor that is given in table 12.2-1. Can anyone shine some light on the issue or any other increasing factor that I have not mentioned.
RE: ASCE 7-05 Increasing Factors (overstrength, redundancy)
The code usually states that the overstrength factor would be applied only where it is specifically required.
I didnt see anywhere that the overstength factor would apply to the diaphragm. When you say diaphragm are you referring to the attachment of the diaphragm to the steel supports?
I've attached a memo that we used on another project and it is for a specific situation - but the logic flow might help you see why diaphragms could be considered as part of the seismic force resisting system: