AC Motor Supply Wye Delta
AC Motor Supply Wye Delta
(OP)
I have a simple question/inquiry. I'm determining the stator supply configuration for a 6.9kV 3-Phase 12-pole squirrel cage induction motor. What are, if any, the pro and cons to supplying the stator with a WYE connection that does not utilize the neutral vice a Delta connected stator?





RE: AC Motor Supply Wye Delta
A delta connected stator for 6.6kV rated motor doesn't seem standard.
If the motor is being supplied directly by a transformer (hope my understanding is right), it doesn't matter whether the transformer winding is delta or star connected (not withstanding whether the motor/stator is star connected or delta connected).
If transformer winding is delta connected, there is no earth reference and earth fault protection based on residual voltage measurement will be necessary.
In case the transformer winding is star connected, the star point can be earthed through NER and current based earth fault protection supplied from neutral CT can be used.
RE: AC Motor Supply Wye Delta
You are correct. This is not a typical motor or motor installation. This will eventually be for offshore marine applications. I'm questioning the motor stator wiring configuration. What are the pros/cons from: a delta wired stator; or wye wired stator where the neutral is either not connected or shorted internally to the motor.
Do I see less eddy currents in a wye connection where the neutral is not connected, or...
This is my question and I'm not sure how else to phrase it. The power supply may be a dedicated generator with a WYE or Delta wired output. Typically on offshore installations, the generator outputs are delta wired.
RE: AC Motor Supply Wye Delta
RE: AC Motor Supply Wye Delta
RE: AC Motor Supply Wye Delta
RE: AC Motor Supply Wye Delta
I am assuming that you are designing a new winding, not just reconnecting a wye wound motor to delta (the latter one will kill the winding).
Having said that, I have seen (and rewound) delta connected 6.6 KV stator windings for 3.5 MW/4 MW boiler feed pump motors. Though many MV motors are star connected (thereby reducing the voltage stress across phase to ground), if the MW is high (meaning more current requiring heavier copper cross-sections, which are difficult to handle), a wye connection is discarded in favor of delta connection.
* Women are like the police. They can have all the evidence in the world and yet they still want a confession - Chris Rock *
RE: AC Motor Supply Wye Delta
Thanks, I can see there is a case for delta connection in MV motors especially in cases where there is limitation on available power supply voltages (like marine applications such as the present case).
jlamann,
What is the motor rating. From protection point of view, I don't see any issue even if the motor is delta connected especially if the CTs are built into each winding of the motor for sensitive Differential protection.
RE: AC Motor Supply Wye Delta
The comments made above regarding stress and diff protection are important as well.
RE: AC Motor Supply Wye Delta
It really does not matter which connection the motor uses.
The bigger factor than this connection is how the motor is built internally to minimize insulation stresses. But unless you are actually building the motor you really have little control over this.
RE: AC Motor Supply Wye Delta
The motor rating is approx what edison123 mentioned.
motorspert-
Those are the type of comments I'm looking for. Thankyou. Are there any potential weight savings by designing/building this motor with either a WYE or Delta stator. If incorporating a Delta stator containing 3rd-order harmonics, the space/weight of a harmonic filter may need to be looked at to remain within power quality limits.
RE: AC Motor Supply Wye Delta
Firstly, the harmoncs are internal, they will not be seen outside the motor and you will not need any filters - apolgies if I have mislead you.
The effect will be second order in terms of temperature
rise and motor efficiency, the motor designer will incorporate this into the design without you realising.
RE: AC Motor Supply Wye Delta
As for 3rd harmonics, there are ways to eliminate them by proper winding design. So, performance will remain the same.
RE: AC Motor Supply Wye Delta
To your question about weight of the motor, I guess it would be lesser for a delta winding motor when compared to star connected.
This is because of the lesser current that the delta connected windings see and hence lesser heat. This should apply even after making provision for additional heat due to circulating 3rd harmonics in delta.
I guess the weight is a factor in off-shore application as is the limitation on available voltage levels.
RE: AC Motor Supply Wye Delta
Star or Delta, total amount of copper is same.
Star = Less turns, more copper cross-section
Delta = More turns, less copper cs
RE: AC Motor Supply Wye Delta
many thanks!
RE: AC Motor Supply Wye Delta
Surely you are not proposing to ground the supply through the motor.
Q Will the supply be Star or some form of grounded Delta?
Roy
RE: AC Motor Supply Wye Delta
3rd harmonics (and its multiples) can be eliminated by using winding spread of 120 deg. The 3rd harmonic vector closes on itself resulting in zero value.
See if you can get a copy of Performance and Design of AC Machines by M G Say.
RE: AC Motor Supply Wye Delta
But advances in insulating material has elimilated that factor. So if there is no cost, weight or size benefit, I do not think there is any tehcnical advantage of star over delta windings or vice versa.
RE: AC Motor Supply Wye Delta
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: AC Motor Supply Wye Delta