Greetings,
I have a project that has a clerestory roof (a high roof) which looks like this:
       |-------------|   
       | High roof   |
--------             ----------

It has a metal deck with rigid insulation, no concrete. It is located in SDC "D". Is there any provision in the code (IBC 2003/ASCE 7-02) that will allow me to use tension only bracing to bring the forces down to the lower diaphragm instead of designing a SCBF or SMF. I have shear walls + steel beams framing this building below the high roof.

Any help is appeciated.

Thanks

RE: Clerestory - Tension Only Bracing

(OP)
Are knee braces allowed in seismic design? particularly in SDC "D".

RE: Clerestory - Tension Only Bracing

Any possibility of continuing four steel columns up from the steel framing below to take the lateral in cantilever action?

I don't know why knee braces couldn't be used, but, if you have room for diagonal knee braces, why not just use small shearwalls?  Seems like the site obstruction issue would still be there with the knee braces anyway.

Mike McCann
MMC Engineering

RE: Clerestory - Tension Only Bracing

(OP)
The roof is about 14' high, which would be the length of my cantilever. Are there any other suggestions?

Thanks

RE: Clerestory - Tension Only Bracing

3 Dimensional tube steel moment frame, pinned at the base?

Mike McCann
MMC Engineering

RE: Clerestory - Tension Only Bracing

I do not thick tube steel moment frame is good option.  R factor is very low (R=1.5 for tube) and it is super hard to have approved moment connection per current code for tube.

Wide flange is first choice if considering moment frame I believe.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources