Hi,

To refer;
Emergency Diesel Engine Generator Package
1500kWe.

Can anyone tell me how to calculate the starting of 185kW motor at 1100kW base load?

And;

What data and formula do I need to calculate the engine capability for the frequency drop for the above loading?

Thank You.

RE: Engine Capability For The Frequency Drop

If this is a droop governor set at 3%, then your frequency will be nominal frequency minus (actual load / rated load x droop {3%})
Rated load = 1500kW
Base load  = 1100kW
Motor load = 185kW
Total load = 1285kW
Actual frequency under load = 103% - (1285kw/1500kW x .03)= 100.43%
On a 50 Hz base, 50 x 100.43 = 50.215 Hz.
On a 60 Hz base, 50 x 100.43 = 60.258 Hz.
NOTE Engine speed under load is a function of the governor, not the engine. If the governor is running in autogenous mode, the frequency will drop below rated frequency when a load is applied and then correct back to rated frequency.  

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Engine Capability For The Frequency Drop

Isn't this the same question you asked in thread237-218709: How to calculate the starting of 185kW motor at 1100kW base load??

Bear in mind that a motor under starting conditions requires a lot of reactive power which is demanding on the AVR. AVRs vary enormously in performance. The behaviour under transient conditions will depend on the interaction between the AVR, the governor, and the load being driven. The dynamic response of the system isn't easy to predict without knowing the characteristics of the machine. David gave good advice in the other thread - is there a reason why you can't follow it? Bill: two answers to the same question? You have a lot of patience!
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources