What is the best to do of the energization of power transformer (11/132 KV , 60 MVA) from primary or secondary side at the live busbar.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Low risk
RE: Low risk
RE: Low risk
Just my opinion, base on few cases was happend at the last mounth.
1. Check first energazing procedure with trafo mnf.
Read this post.
thread238-218517: Trafo inrush current.
2. Check all fire systems and gas.
2.1 check place of fire services hydrants and water.
2.2 check push button " fire trouble" and check that this operation disconnect all power supplies.
2.3. Put guys from fire service near to this hudrants with your electrical guys.
2.4 please order one or two mobiles of fire service
3. Check "place" of oil in case of trafo fault.
4. Check option of energazing trafo from very weak line, with lowerst level of SC., if trafo mnf. haven't some special requerements and you have option --energize from low side
5. in additional to diff 87T trafo protection and 50/51
add temprorary 50/51/50N/51N settings with minimum time settings on the infeed line.
Just my opinion.
Best Regards.
Slava