i understand that this is a extensive topic, yet i hope someone could explain the following:

how do you calculate pump head and select booster pump based on that ?

thank you

RE: Pump head calculation/pump selection

pump headis given in ft and is proportional to the differential pressure in pounds per square inch (PSI) based on the fluid being pumped density.  So water with a 62.4 lb/ft^3 density when you divide 62.4 by 144 in^2 per ft^2, you get .433 psi per ft.  Now multiply the pumps head from the chart at the flowrate you desire.  Say the pump will put up 30 ft at 20 gallons per minute, that means 30 times .433 = 13 psi differential across the pump.

You can work backwards too.  Say the system requires a pressure of 74 psi and the feed water has a pressure on 25 psi.  so 73-25 = 48 psi.  divide 48 by ,433 to get 111 feet of head. look for a pump that has 111 or more feet of head at your desired flowrate.

RE: Pump head calculation/pump selection

You need to find where you require the most pressure.  It is usually the toilet/urinal flush valve on the highest floor.  But don't neglect the farthest fixture if you have a system with a long run.

Flush valves typically require 35 psi to work effectively.

Find out the static pressure at your inlet.  Typically a fire department hydrant test will determine that.

With all that in mind, determine the pressure drop (friction losses_ in your system - don't forget the backflow preventor which is typically 10 psi at the flows you will see.

The difference will give you the total dynamic head the pump has to provide.

You will need to know what flow you will want.  You will need to know a typical flowrate that you can size the pump to, but you will also want to determine the maximum flowrate so you can make sure you have enough pressure at that flow to flush the aforementioned toilet.

Think about constant speed pumps and variable speed pumps.  I prefer the latter and their price is fairly competitive now.

After that, contact the pump manufacturer and see what he thinks.   

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources