Vent Header Isolation and Diversion
I currently have a relief vent header (potentially containing a flammable gas stream) that is routed to a scrubbing system and subsequent downstream processing.
Under certain circumstances (ie loss of scrubber water flow) there is a requirment to 'bypass' the scrubber and downstream processing line and relieve the vent header locally by an automatic switching of isolation valves in the header.
Obviously by having automated isolation valves in the header there is a potential that the switch over does not work properly and the header line is isolated with both outlet valves closed thus redering the relief devices that relive into the header useless.
Are there any standards that state this cannot be done as it could potentially isolate a relief device?
If it is acceptable are there any standards that cover how reliable the switch over valves need to be?
RE: Vent Header Isolation and Diversion
I2I
Whenever the system equipped with "automated" diverter valve, the failure of the diverter valve will lead you to have additional ultimate safeguarding. May consider manual operation with interlock like interlocking system for 2 x 100% PSV inlet & outlet isolation valves...