Contorl Valve Help
Contorl Valve Help
(OP)
Hi All
I need to connect a butterfly valve + elctro pneumatic acutator to the Bialey DCS. But in order ot make it run ON/OFF . How many wires do ineed to run from the valve to the junction Box and to the terminal room.
Is one dekron wire enough?
I need to connect a butterfly valve + elctro pneumatic acutator to the Bialey DCS. But in order ot make it run ON/OFF . How many wires do ineed to run from the valve to the junction Box and to the terminal room.
Is one dekron wire enough?





RE: Contorl Valve Help
For modulating valve you will need 1 pair of shielded wires 28 AWG or greater.
Roy
RE: Contorl Valve Help
If that is what you have, then a two wire cable is all you need together with the software set up to ask for 100% open and 0% open. This assumes you dont need limit switch feedback.
RE: Contorl Valve Help
However it would be good to know what you meant by "elctro pneumatic acutator" as this could be loosely interpreted as a solenoid (on off in nature), or e/p positioner (modulating in nature)
If it is the former, then you will need a relay output from the DCS with a source of power to match the solenoid rating.
If it is the latter, then you will also require an air supply and the to operate 4-20mA as "on/off" it would reqire the signal to come from a control output from the DCS system. The PID settings in the controller would also have to be set with an infinitely small proportional band and no integral or derivative action.
I trust this helps,
Mlv
http://www.coulton.com
RE: Contorl Valve Help
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Contorl Valve Help
I accept that if your "elctro pneumatic acutator" has a solenoid fitted with a suitable coil rating, which can be fed directly from the DCS digital output, then I would agree with Scottyuk that a simple transfer block with a digital flag would be more appropriate.
So it still comes down to what is meant by
"elctro pneumatic acutator"
I trust this helps,
Mlv
http://www.coulton.com
RE: Contorl Valve Help
I agree - we are missing some important detail here!
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Contorl Valve Help
Roy
RE: Contorl Valve Help
----------------------------------
If we learn from our mistakes I'm getting a great education!