Yoga Studio

Yoga Studio

Yoga Studio

(OP)
I am renovating a room into a yoga studio that requires a room temp of 100 degrees F. Its called a hotbox.

The room has a existing rooftop unit, however the burner is larger than required.

If I return air through the rooftop unit, [the burner has a delta T of 65 deg. F], the discharge temp will be 165 deg F (based on a return air temp of 100 deg F). The unit has a thermal cutout set at 150 degrees F, so I believe the unit will shutdown.

I am trying to make this unit work somehow. A couple of things:

- if the room setpoint is 100 deg F, the return air temp will be less than 100 deg F (based on heat given up through the room), however, the room is well insulated (we are using freezer panels) so I don't think that much heat will be given up.

- I am using about 30% outdoor air which helps in the wintertime to lower the mixed air temp to the heat exchanger

I am looking at ways of making things work, but I am pretty sure there are no options (especially in  the summertime).

Any ideas?

RE: Yoga Studio

I agree with Don above.  Electric heat is the way to go, either with radiant panels or a duct heating coil.  The gas burner is just too much.  It is swatting a fly with a sledge hammer.

RE: Yoga Studio

Or something interesting with a small heat pump with two condenser coils.  

Evaporator coil for humidity control.  One condenser coil in series with the evaporator for reheat.  Second condenser outside to reject anything left over.

RE: Yoga Studio

Gas burner is to much????  Heat is heat and there are plenty of options regarding modulating gas heaters.  However, for this situation... the electric heat option is probably the easiest to implement.

RE: Yoga Studio

A gas-fired tankless water heater with in-line circulating pump and fin-tube radiators with 3-way valve on pump suction is an option using gas to provide independent supplemental heat.
Check out www.takagi.com japanese manufacturer.
They offer 85 % efficiency water heaters and they are proven to be work horses. I have such a water heater that I use for domestic water and it works great, highly reliable.
I think you can find them in a condensing type model as well (mainly european models).

RE: Yoga Studio

moving more air would result in a lower delta T. can you re-sheave the fan to move more air? increase the OA percentage to keep the room temp constant. not the most energy friendly, but maybe the cheapest solution.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources