3/4 head in 10' and above ceiling?

3/4 head in 10' and above ceiling?

3/4 head in 10' and above ceiling?

(OP)
i was always told that in a ceiling above 10' use a 3/4 head is that true or am i able to still use a 1/2 head? is it all based on k-factors? are they using 3/4 cuz of the flow?

RE: 3/4 head in 10' and above ceiling?

There is nothing in NFPA 13 that I am aware of that would require a K8 or larger sprinkler in a ceiling >10'.

Travis Mack
MFP Design, LLC
 

RE: 3/4 head in 10' and above ceiling?

The K factor for densities for storage occupancies may get you to a 3/4" sometimes. Take a look at NFPA 13, 02, 12.1.13 0n page 108.

Densities less then .20 use a K of 5.6
.20-.34 K of 8
.34 or greater K of 11.2 or >

So if u are greater then a K 11 it will be 3/4", most K 8 and 5.6 can use a 1/2".

Do not know if this helped at all.

****************************************
Fire Sprinklers Save Firefighters' Lives Too!


 

RE: 3/4 head in 10' and above ceiling?

I hope we are not talking pipe nipple sizes. NFPA 13 requires a 1-inch nipple.

On my watch, I wouldn't accept what you guys are talking about, unless we are discussing the final union fitting.

 

RE: 3/4 head in 10' and above ceiling?

LCRep

Did you get my e-mail on your upcoming sweaty Texas holiday?

RE: 3/4 head in 10' and above ceiling?

Scott:

I believe he is talking about utilizing a minimum K8 sprinkler (3/4" thread) in anything that has a ceiling greater than 10'.  For 10' and less, it would be a K5.6 (1/2" thread).  That was my assumption.  And yes, any drop feeding those sprinklers would be a minimum of 1".

I vaguely recall a requirement from Las Vegas that when they had ceilings >20', they required a minimum K8 sprinkler.  I further believe that they also made you increase the design area to 100x the ceiling height.  So, a 25' ceiling in a casino lobby would be K8 sprinklers and a 2500 sq ft design area.  I am not 100% sure on that.  

However, there is nothing in NFPA 13 that mandates a K8 sprinkler when your ceilings are >10'.  The only time that NFPA 13 mandates K factors is due to increasing densities.

Take care!!!  Have a great weekend.

Travis Mack
MFP Design, LLC
 

RE: 3/4 head in 10' and above ceiling?

Stookey,

Check your work e-mail.

Tom

****************************************
Fire Sprinklers Save Firefighters' Lives Too!


 

RE: 3/4 head in 10' and above ceiling?

(OP)
thanx everyone for ur responses, maybe then its just something my dad does just to kill an area, cuz i know he always says >10' use 3/4 heads but now i am engineering i was doing a vaulted ceiling and i had 3/4 heads in there and some of my co workers were asking why. i just thought something was in nfpa about that. oh well thank you tho.

RE: 3/4 head in 10' and above ceiling?

LCREP

Got it, worked it out, and I look forward to seeing you and your family at the end of June.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources