Gauge Size
Gauge Size
I would like to use a 28 awg shielded cable over a distance of 50 meters. Will it work? Or is it better to use 22 or 24 awg.
This is for trasmission of digital and 4-20mA analog signals.
RE: Gauge Size
RE: Gauge Size
I am not quiet sure what a 0.21 volt drop means in this context?
You said in your example that 1/2 volt drop would be OK for your example, what threshold are considering when stating that?
RE: Gauge Size
TTFN
RE: Gauge Size
RE: Gauge Size
Save the attitude ask questions instead.
Doing your resistance calc did you include both directions?
Compliance is the standard term for voltage over the minimum needed in a 4-20mA signal chain.
Since it is a CURRENT loop voltage just tags along and makes everything work - its value doesn't matter precisely.
You have a power supply that puts out some voltage to run your loop. Say 24VDC
Then you have a sensor that needs to see the 4-20mA signal. It will consume/demand some of the voltage lets say 10V now you have 14V left or available for other voltage drops in the loop. Like your wire size voltage drop. If that wire were much longer and added up to 14V you would be out of compliance voltage and the circuit would not work.
IRstuff is just surmising that 1/2V is not likely to knock most systems out of compliance.
Keith Cress
RE: Gauge Size
Dan - Owner
http://www.Hi-TecDesigns.com
RE: Gauge Size
RE: Gauge Size
RE: Gauge Size
not constant current
Keith Cress
RE: Gauge Size
Anecdote. We had a loop with a theoretical device load of about 22 volts at 20 ma. The input resistor on a replacement alarm relay was off spec. As a result, the 24V power supply could not develop 20 ma. across the loop. We became aware of the problem when the shutdown alarm failed to function in an over temperature event. The stainless steel thermo well in a 100' stack was melted off. Fortunately the refractory material held up. One crack in the refractory and we may have lost the stack.
Yes, voltage ratings of the devices in a loop are important, as is a field check of device calibration and function, rather than a quick and easy shop calibration.
Bill
"Why not the best?"
Jimmy Carter
RE: Gauge Size
e.g. Rosemount 3051 Pressure Transmitter
Max Loop Res. = 43.5 (P.S voltage - 10.5)
So at 24 VDC you are allowed 587 Ohms
Assuming your reciever is 250 Ohms then your cable can be 337.
So 28 AWG would be good for a very long way.
You can also boost the PS voltage up to allow even greater distances.
Hope this Helps
Old Instrument Guy