What are the guidelines on how many soil borings to take for a building structure. Are there rough square footage or spacing numbers to determine a minimum number of soil borings?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Soil Borings
No. of Borings depends on:
1. Size of the structure
2. Configuration of the structure (area vs. perimeter)
3. Variation in load characteristics from one part of the building to another.
4. Budget constraints
5. Experience with other structures in the area.
6. Availability of other borings in the area or on the site.
7. Requirements of local building codes.
8. Requirements of governmental agencies.
The BOCA code once required one boring for each 2500 sf of building.
The FHA and HUD agencies used to (don't know about today) require one boring for each 60 feet of perimeter for buildings more than three stories, and one boring for each 100 feet of perimeter for those less than three stories (basements count as a story).
One recommended guideline was:
Buildings less than 5000 sf: Min. 2 borings
5000 to 20,000 sf: 2 to 4 borings
20,000 to 40,000 sf: 4 to 6 borings
40,000 to 60,000 sf: 1 boring for each 10,000 sf plus 1 boring for each 800 feet of perimeter
over 60,000 sf: 1 boring for each 15,000 sf plus 1 boring for each 1,000 ft of perimeter
Add 1 boring for each special installation such as chimney, elevator pit, concentrated machine load, extra deep basement, high sign, etc. unless it occurs where a typical boring occurs.
RE: Soil Borings
Another thing to know to, is what are the expected loadings and/or height of the building. These will impact how deep the borings need to go.
Also keep in mind, if the borings are far apart and one boring shows a deep area that would need to be excavated do to poor soils, there may be more excavating being recommended than might otherwise be needed, closer borings could narrow in the bad area. Or you could do more borings later.
RE: Soil Borings
f-d
¡papá gordo ain't no madre flaca!
RE: Soil Borings
guidelines on depth would be interesting. Have any?
RE: Soil Borings
for pier footings - 2 times the anticipated width.
for strip footings - 4 times the anticipated width.
look at the grading plan as if there is a 10 ft cut and the bearing grade is 2 ft below that you need to drill 12 ft before you get any foundation design data (you will have 12 ft of data for your earthwork evaluations though).
Understand the geology: If there is a soft clay layer at 2 times your foundation bearing depth, you really need to fully penetrate the soft clay before you terminate the boring.
There is somewhat of a chicken and egg problem here. You need to have some perspective on the column loads and general sense of bearing pressure. So, if 2,000 psf is a safe bet and you have 200 kip column loads, your footing needs 100 sf (10 ft square). That relates to a 20 ft boring below the anticipated bearing grade. If you start by anticipating 4,000 psf, you'd end up with a shallower "design" boring depth, which may prove too shallow.
Hope this helps.
f-d
¡papá gordo ain't no madre flaca!
RE: Soil Borings
if i suspect old fill, the borings are tight...if i suspect residuum, then spread them out. i typically use 50x50 and 100x100 as starting points (depending on the size of the building--wouldn't likely do 50x50 on a million sf building). start with identifying the max anticipated loads, history of site, topo maps, etc and go from there. consult a geotech that is familiar with local conditions.
RE: Soil Borings
If one was going to have to use piled foundations - especially if friction/adhesion piles, then you would go at least 2 to 3 x the likely dimension of the pile cap (i.e., the perimeter of the pile group) below the pile tip (see Tomlinson and others for zone of influence of settlement for pile groups). This would be modified of course should you "hit" rock or glacial till/drift, etc.
Sampling, in my world, would be at 2.5 ft intervals to 15 ft then at 5 ft intervals to 50 then space at 10 ft (as general rule). The 2.5 ft intervals is to ensure that you have sufficient samples in the footing zone (or, for thoses strutures with basements) to make a reasonable assessment of the soil properties (sufficient N values - or torvane values in tips of undisturbed samples). Oh, and dig a few shovel pits to ascertain, with some precision, the thickness of topsoil (important from a construction/stripping point of view).
In India, I ran a combination of 4 inch thin-walled tubes at the metre interval, then dropped a standard split spoon down the thin-walled hole. This way I covered 900 mm of the 1000m intervals. Because we were very interested in the upper 6 m or so, we did this for 8 m before increasing the sample spacing.
Getting back to the geology. I was on a site that had 30 to 35 ft of very dense sand and gravel. Good stuff, eh? A previous job (by others) in the same area had, oh, a large area fill of 10 to 15 ft involved with the structure - on one side. Mmmm At 35 ft, 100 ft of soft compressible normally consolidated "fat" clay (for you fattdad, mon ami). Can you guess what happened after the previous structure was built (say 3 to 4 years later)??
So, know your geology, know your development/structure, understand the influence that the likely foundations will have, and taylor your programme accordingly. Guidelines are only that - experience rules. Also, always have a geotechnical techician or engineer (junior to intermediate) log the boreholes - do not rely on the drillers.