Do medium voltage (5-15kV) cables (shielded power cables) "swell" over time when subject to constant moisture, laying in water?
If this "swelling" is evident, is it indicative of the remaining life of the cable?
Thanks

RE: Cable Swell

They shouldnt swell, if they do you might have a problem. Conduct a Tan Delta test.  

RE: Cable Swell

I had problems with MV cables swelling, but the "water" in question had a high amount of various interesting hydrocarbons incorporated.  Interstingly, the cable remained in operation until it was "blown' by a goof-ball who was "testing" it with a DC Hipot.

old field guy

RE: Cable Swell

Water in the conductor will make them swell.  It's not uncommon.  Most cable companies have proceedures for removing the water.  

RE: Cable Swell

N2 purge, I have that procedure around here somewhere

RE: Cable Swell

we have had a number of aluminium conductor cables swell and ooze a white fluid (al oxide) due to moisture ingress.  The outer sheath ends up splitting, and exposes the conductor to the earth, which then adds a OHS risk to staff or contractors digging in certain locations around this problem - people getting tingles off shovels and crow bars etc.

 

RE: Cable Swell

(OP)
Wow this is very interesting. I wouldn't have believed it until I saw it myself,and now I know it is possible.
I assume the cables would need to be completely accessible to remove the water, which is unrealistic in my case.

RE: Cable Swell

If water gets into aluminum cable, and sits there long enough for aluminum oxide to form and swell, the remaining life is pretty close to zero.  I don't think you'll ever purge the water out adequately and aluminum oxide is a lousy conductor.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources