×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Fused Low Voltage Circuit Breakers

Fused Low Voltage Circuit Breakers

Fused Low Voltage Circuit Breakers

(OP)
Can limiters be put the load side of low voltage power circuit breakers? I have alawys seen them on the line side. Is there an associated standard like NEMA or ANSI for this application. The reason that we want to put the limiters on the load side is because we are doing a retrofill job where the old breakers are old FPE breakers with fuses on the load side.

Thanks

RE: Fused Low Voltage Circuit Breakers

Limiters are "limiter Lugs" usually used for multiple sets of low voltage cable protection. I guess you mean current limiting fuses which gave the basic FPE circuit breaker a higher interrupting rating.
If you are retrofitting or replacing the breaker first you neeed a short circuit study. After that is complete, you will see what you need for interrupting capacity.
The application may not require fused circuit breakers.
JIM

RE: Fused Low Voltage Circuit Breakers

If you are doing a retrofill with high interuption requirements why wouldnt you do a vacuum retrofit? Costs about the same with little maintanance requirements.  

RE: Fused Low Voltage Circuit Breakers

I've never seen them on the load side. Normally the original manufacturer would dictate such things. I would not want to change the original design if I could avoid it.

RE: Fused Low Voltage Circuit Breakers

There are some circuit breakers with a "fuse block" on the output side. This block basically attaches right into the breaker and extends the output side of it. It allows for a higher interrupting rating. However, this is a factory option only. There's no standard that I know of for installing your own fuses. The rating of the breaker is what it is. It is still upstream of your higher rated fuses.
 

RE: Fused Low Voltage Circuit Breakers

But...
If your goal is not to provide added protection OF THE BREAKER but rather the downstream system, then I don't see a problem with that. In other words, if your existing breaker is already rated for the available fault current, but you want to limit the fault current down stream because other equipment cannot withstand that level, then current limiters are a legitimate choice, maybe your only viable choice.

You need a full detailed coordination study before embarking on any of this.

RE: Fused Low Voltage Circuit Breakers

I agree with jraef. I would emphasize that if there is concern for the interrupting duty of the breaker, the manufacturer must be consulted for the proper time-current curve and placement of protectors. At high fault currents, physical location can be important to the performance of the breaker.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources