laundary air conditioning
hi guys ,,
i ve asked to air conditioning a five stars hotel laundary which service guests rooms, hotel appartments,... a list of equipment of the laundary has been supplied to me like steam heated extractor 40KG and ironer ...etc. and the steam consumption mass flow rate for all these equipment are shown how can i calculate the load of the laundary ?i ll use hood for ironer .i have looked at ashrae for these application and i found nothing
RE: laundary air conditioning
The heat load to the space will equal the steam consumption of the equipment, unless the equipment is hooded and extracted.
As with you, the larger laundry facilities were in 4 and 5 star resorts with large chilled water capacities - which was a plus.
Andy W.
the load dissipated to air which the cooling coil shoul handle = hfg steam x steam mass flow rate is that right
hfg steam =2133.4 kj/kg @ 3 bar
is this right??
"hfg steam =2133.4 kj/kg @ 3 bar" - (gauge) yes. Note that the tables are usually in absolute figures.
If you have large dryers, and you are responsible for exhausting them, allow for lint build up in the extraction ducts. Make sure there are clean out doors installed so the ducts can be checked and cleaned.
I recently did a rip out, and re-install on a bank of 4 large dryers in a laundry room of a hotel and found 15 inches of lint in a 30"x 30" duct for a distance of 30 feet.
It was not supposed to be there because the dryers had pre filters. However the maintenance practices at the hotel left a lot to be desired. I will not say any more than that.
B.E.