Construction loading of slab-on-grade

Construction loading of slab-on-grade

Construction loading of slab-on-grade

(OP)
To finish a combination asphalt and concrete road network, the contractor wants to use a construction process which slipforms the curbing first, then places the 10-inch thick reinforced concrete turnpads at intersections, followed by the asphalt paving between the concrete turnpads. Question is how long should the contractor wait before placing construction loads of the paver and loaded asphalt trucks on the concrete turnpads. f'c = 4,000-psi with #3 bar both ways at 12-inches O.C. Your perspectives please!

RE: Construction loading of slab-on-grade

When the field cured cylinders, (under a tarp on top of the turnpads), achieve 90% of F'c.  Probably 14-20 days depending on temperature.

RE: Construction loading of slab-on-grade

depends on the subgrade, subbase and base conditions as well as the strength of the concrete paving.  10 inch thick with 4,000 psi concrete and reinforcing seems like a lot.  were the turn pads overdesigned?  If so, then maybe you don't need to wait so long.

RE: Construction loading of slab-on-grade

(OP)
Thanks guys! Here's some more info.
- Allowable soil bearing capacity = 3,000 psf
- Minimum 24-inch thick subgrade compacted to 95% modified proctor for both asphalt and concrete areas.
- 4 1/2-inch thick base course of 2A modified (well-graded crushed stone) aggregate compacted to 95% modified proctor for concrete areas.
Turnpads and roads were designed for traffic loads of military vehicles up to 70 tons.

RE: Construction loading of slab-on-grade

first, decide if you can allow something less than 4,000 psi for the construction load.  Common design for freeways is only 3,000 psi at 28 days.  Then ask the supplier to provide data on 3-, 7- 14- and 28-day strengths and plot your curve.  See if you can't get to about 3,000 psi after 10-days.  If you really want to speed things up, go with a high early strength mixture, you can get up to 3,500 psi in 24 hours.

http://www.pavement.com/Concrete_Pavement/Technical/FATQ/Design/High_Early_Strength_Concrete.asp
http://www.pavement.com/Concrete_Pavement/Technical/Fundamentals/

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources