Have a new project - 47 individual three story townhouse structures in a complex - with three to six townhouses per structure.
For fire separation reasons, the floor diaphragm between the units must be discontinuous, but the roof diaphragm is continuous. This will leave a 1/2" to 1" full height separation in the party walls from the foundation to the underside of the roof diaphragm.
Properly applying the wind forces in this condition I have no problem with. My problem comes in properly applying the seismic forces considering the link of the roof diaphragm. It seems to me that due to that link, more force than normal will be thrown to the roof diaphragm than just analyzing each townhouse separately, because they could deflect differentially, causing hammering without the roof diaphragm link. This implies a need for stiffening at the roof diaphragm level to prevent hammering.
My question is if anyone has run into this condition before, and how did you quantify and detail the seismic link problem at the roof?
For fire separation reasons, the floor diaphragm between the units must be discontinuous, but the roof diaphragm is continuous. This will leave a 1/2" to 1" full height separation in the party walls from the foundation to the underside of the roof diaphragm.
Properly applying the wind forces in this condition I have no problem with. My problem comes in properly applying the seismic forces considering the link of the roof diaphragm. It seems to me that due to that link, more force than normal will be thrown to the roof diaphragm than just analyzing each townhouse separately, because they could deflect differentially, causing hammering without the roof diaphragm link. This implies a need for stiffening at the roof diaphragm level to prevent hammering.
My question is if anyone has run into this condition before, and how did you quantify and detail the seismic link problem at the roof?
Mike McCann
MMC Engineering






RE: A New One On Me
RE: A New One On Me
RE: A New One On Me
RE: A New One On Me
I have not designed this type of structure in the US, but
the Australian codes specifically allow for the floors of these types of structures to be connected together as long as there is solid timber between the fire rated walls above and below.
If you could justify that the charring width of a solid piece of timber gave equivalent fire resistance to the walls above and below, could you then apply for a variance based on that?
Of course there may be associated sound transmission issues.
RE: A New One On Me
It's interesting to me too in that it seems like the structural integrity of the building is being trumped by the fire requirements.
I've asked for the specific code section requiring this disconnect to see if it is interpreted properly, but, in lieu of that, I'm wondering how to analyze it.
Could use the computer, I guess, but was looking for a hand method to keep the analysis method simple.
Mike McCann
MMC Engineering
RE: A New One On Me
RE: A New One On Me
I would think the intention of not linking the floors is to prevent progressive collapse due to thermal/fire failure in any one unit from spreading to adjacent units (or to the party wall).
But, if you make a connection at the front and rear walls, the corners can be self braced enough to prevent this progressive collapse.
If this works, the diaphragm span from front to rear wall should have a small amplified deflection that might be less than the 1" provided.
RE: A New One On Me
RE: A New One On Me
We modelled the variance request from code language in Oregon:
http://w
Very good point about the sound rating! Now they can choose between quiet units or paying more for the shear walls/holddowns.
RE: A New One On Me
Apparently, according to the local jurisdiction, I will have to live with the floor diaphragms being cut. They are all wood structures, with steel W shape frames at the lower garage door end. I guess this is a requirement for condos now.
Most structural engineers are just ignoring the continuity of the roof diaphragm from what I understand. I guess there will be a lot of similar struuctures out there with roof damage after our next big one here. Not my idea of good engineering.
I do not know the deflection yet at the roof if it is cut too, but I am leaning that way, essentially pressing for a flexible seismic joint at that location and increasing the separation up to 2 or 3", whatever it calcs out to be. I will be forced to design each townhouse individually for wind and seismic. The Architect is going to love to read this flexible joint going up the roofline. Oh well... What do I know...
Thanks for the comments guys.
Mike McCann
MMC Engineering
RE: A New One On Me
"If you are going to build a Townhouse per 2006 IRC Washington State
Amendment R317.2 Townhouses. Each Townhouse shall be considered a separate
building. R317.2.4 Structural Independence clearly states that each
individual townhouse shall be structurally independent. The commentary code
book explains that the middle townhouse unit may burn to the ground and this
loss will not affect the remaining units both structurally and existing fire
resistance. The exceptions indicate that the roof and wall sheathing may
fasten to the common wall framing, but each unit will have it's independent
shearwalls, fire-resistive rating to include rated roof sheathing.
So, can lateral restraint (shearwall) be shared by two or more townhouse
units? No. Can other measures (gravity elements beams and headers) be
shared between units? No per IRC R317.2.4."
So, I will have to analyze the units individually verticallyn and laterally, and provide a structural T/C link between the units at the roof - no seismic joint.
With the roofs not moving differentially, I see that there will be still be some differential movement between the units at the floor levels increasing and decreasing the 1" air space, but I cannot put a finger on how to quantify that movement at the moment. I think that I'll increase the air gap to 2" and think about the solution some more.
This structure is going to behave in a very strange way. Apparently, the purpose of the IRC reg is that if one unit burns to the ground, the vertial and lateral components of the adjacent units remails intact.
That's great for the two adjacent units, but what about the 47 units affected with leaks at the roof by the earthquake, causing mold in the interstitial space between the units due to the lack of proper ventilation?
I'm going to have to write a letter to the owner expressing my concernsand have him sign it.
Mike McCann