ITE CR Frame Switchgear?

ITE CR Frame Switchgear?

ITE CR Frame Switchgear?

(OP)
I've come across an ITE device (switchgear?) labeled CR30.  It's a 480V 2000A breaker in an FS-20 switchboard.  Seeing as the device is older than I am, I'm having difficulty finding specs and operation on this.  Does anyone have information on this device?  A little more information... CAT NO. ATI-CR30, w/ Amp-Trap Model A6CRA. Circa 1976-1978.

I'm trying to conduct an arc-flash study.  We were unable to remove the panel to inspect the device more closely because I left my bomb suit in Baghdad thinking I wouldn't need it again.

Thanks all!

RE: ITE CR Frame Switchgear?

You just need curves? What software are you using? What specs are you looking for?

RE: ITE CR Frame Switchgear?

Well, although Siemens bought ITE 25 years ago, that predates your gear by another 7 or 8 years, so it's doubtful much exists on it.

But you are getting a little luck here. I work for Siemens and have here with me a 1977 Goulds ITE catalog. The CR Series MCCB was a 2000A frame current limiting breaker, but used Amp-Trap fuses inside of it for the current limiting. The entire assumbly was rated for 235kAIC Asym, 200kAIC Sym at 480VAC. The fuses they ALL used were that AT1CR30 and you may be able to go back to Ferraz Shawmut for a fuse curve on that. Unfortunately Goulds did not put the curves in the catalog, and that is all I could find.

RE: ITE CR Frame Switchgear?

(OP)
jraef, I've managed to make contact with another Siemens person in the meantime.  I haven't had much luck with Shawmut on obsolete stuff; if it isn't current they won't provide info on it.  They wouldn't provide info in the past on ATS-DE fuses because they were obsolete and didn't have curves anymore.  I'm not recommending them to any clients anymore.

Zogzog, I'm using SKM PTW and I need the curves, but I would also like some background operation info on the breaker.  I may need to recommend a retrofit if possible.

Thank you both.

 

RE: ITE CR Frame Switchgear?

I cant find the curves either, I do have a CR3-2000A breaker (Not CR30)here, dont know about a retrofit unless there is a relacement available.  

RE: ITE CR Frame Switchgear?

SJB, I have 11x17 sets of curves for the older ITE Gould vintage breakers at the office. IIRC the fuse curves are in it as well. I will not be back in until Tuesday, I could scan it for you then.

The current replacement (if not obsoleted already) would be the Siemens CRD6 series, Cat#CRD63B2000, This would require new mounting hardware aswell. You should also have the client  consider replacing the switchboard, as you already are finding out the CR3 frame and fuses are very scare today.

Mike

RE: ITE CR Frame Switchgear?

I have several CR3 frame breakers, not that scarce.  

RE: ITE CR Frame Switchgear?

Hard to find is what I do best. That curve is a rare find, thanks.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources