I'm designing the electricl lighing and exit signs for a stairway in an office building.  I have spec'ed out exit lights and stair lights with battery backup in each fixture.  My question is because I have battery backup in each device, do these fixtures have to be feed on their own circuit? or can I just tap of an existing circuit?

RE: Emergency Lighting

Emergency lighting should be fed, is possible from the same circuit as lights in the vicinity -- if the breaker trips, or something else happens and the lights go out, you still have some.

That said, check your code!

RE: Emergency Lighting

NEC requires emergency light fixtures to be connected to the local lighting circuits, tapped ahead of the light switch.

If dedicated circuits are used, they and normal light circuits need to arranged such that loss of any one circuit shall not cause loss of all normal lights in the area.

 

RE: Emergency Lighting

Look up NEC 700 and NFPA 101.

RE: Emergency Lighting

(OP)
Correct me if I'm wrong.  700.15 states "No appliance and no lamps, other than those specified as required for emergency use, shall be supplied by emergency lighting circuits.

In my case the battery is the "emergency circuit"  so the "normal supply circuit" can feed the emergency lights along with the hall way lights leading up to the stairway.

RE: Emergency Lighting

Your emergency circuit is actually the battery source in the battery pack you mentioned. The tap from the normal light is only to the charge the batteries and is not the emergency circuit. Normal power does not light the "emergency light" when normal power goes out!!

 

RE: Emergency Lighting

Australian standards require a test facility where you can de energise all the emerg. luminaires to test their battery packs. This is very commonly done by having all the luminaires on the one circuit.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources