I have an issue involving the transfer of n-heptane from a tanker truck to a 15Kgal stainless storage vessel.  

Question 1:  what is the recommended velocity of fluid (heptane) through this distribution system (static buildup prevention)?  The system was designed for 5ft/sec, but I cannot find a reference in NFPA to back this up.  5ft/sec is mighty slow.

Attributes of system (to preclude addn'l questions):
Nitrogen powered diaphragm pump,2" sch10 316 stainless piping, gounded/bonded throughout, Nitrogen blanketing on tank.
 

RE: Pumping n-heptane

5 fps isn't too slow.  That's right about where it should be a small diaphram pump (NPSH acceleration head).  

Through a 2" pipe, how fast are you going to fill anyway???

http://virtualpipeline.spaces.msn.com

"What gets us into trouble is not what we don't know, its what we know for sure" - Mark Twain

RE: Pumping n-heptane

Al...

I agree with "Biginch".... 5 fps seems reasonable

According to my trusty Crane 410, 5 fps in a 2"NPS pipe gives you a flowrate of about 55 gpm.

That means a 4000 gallon truck will fill in ~ 72 minutes.

"Mighty slow"...???

NFPA is not going to tell you how to design your piping systems

-MJC

   

RE: Pumping n-heptane

Be aware that a filter or strainer in the line may generate a charge that will need time to dissipate. Hightly purified hydrocarbons need a long time for a charge, once generated, to dissipate. Check OSHA regs 1910.106 which require fill pipes to terminate within 6" of  the bottom of the tank for some classes of liquids.

HAZOP at www.curryhydrocarbons.ca

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources