When people specify aluminum jacketing and insulation for outside refrig or chilled water piping, what is the insulation underneath.  Is it better to use like a foamed plastic Rubatex or urethane Armacell?  They are not just stuffing fiberglass wrap and then putting aluminum around it are they?  What is the best insulation for piping outdoors?

Thanks

RE: Pipe Insulation

I've never seen anything but Armaflex or equivalent.  Needs to be weather resistant, which fiberglass is not.  I'm sure that fiberglass could be used, but keeping it dry is a problem.

The aluminum jacket will keep it from UV damage, make it last even longer.

My experience and opinion only -- let's see what the others have to say.

Goober Dave

 

RE: Pipe Insulation

For exterior low temp refrigeration piping (50F or lower) we always use either styrofoam or isocyanurate, no fiberglass.  But even more important than the insulation is the vapor barrier, which is either ASJ paper or Saran for straight runs, mastic for the fittings.  Then the aluminum jacketing goes on.  Check the Dow website for good info on insulation & vapor barriers.

RE: Pipe Insulation

On external CW & HW we would use Fiberglass piping insulation (Knauf) with PVC jacket (Zeston) or if an older style spec call for Aluminum jacket (Childers). Check 90.1 or the IEC to determine the insulation value.

DX can use a armaflex design with latex paint or jacket to minimize UV degradation.

RE: Pipe Insulation

Fiberglass for CHW is OK for locations in a dry climate. Definitely good for condenser water, not much sweat there. Cellular glass should be used for CHW in humid climates.

Of course, PVC, Aluminum or even stainless steel jackets as indicated above are the norm.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources