There is some discussion going on in our organisation regarding the field pneumatic pressure/leak-tightness testing requirements post assembly of shop hydrotested piping spools. In this instance, the service is fuel-gas, on an offshore gas production platform.
I have read through ASME B31.3 (the applicable code in this instance) and others (ASME PCC-1 & PCC-2 etc).
I hold a belief, from first-principles origin, that the assembled piping system should be leak tested to design pressure. I hold this conviction for several reasons:
1. The gross structural integrity of the piping spools has already been proved during the shop hydrotest, hence risk of explosive failure is negligible or zero.
2. I think it would be quite possible for a flange joint assembly to be field-assembled sufficiently tight to withstand a low pressure leak test (say 35% design pressure, per PCC-2), but not tight enough to necessarily be leak-tight at full design pressure. At design pressure, internal pressure could load insufficiently preloaded flange bolts and unload the gasket, leading to leakage.
3. If design pressure is intended to be a credible pressure-temperature combination with the process fluid, then there should not be any fear of taking the system to this operating point with an inert test gas.
As mentioned, I have searched reasonably extensively, but cannot find any code or standard to support this view. Furthermore, the ASME codes seem to hold to the view that low-pressure sensitive leak tests are adequate proof of joint leak-tightness.
What is the general consensus and practical experience of field installation of prefabricated piping spools?
I have read through ASME B31.3 (the applicable code in this instance) and others (ASME PCC-1 & PCC-2 etc).
I hold a belief, from first-principles origin, that the assembled piping system should be leak tested to design pressure. I hold this conviction for several reasons:
1. The gross structural integrity of the piping spools has already been proved during the shop hydrotest, hence risk of explosive failure is negligible or zero.
2. I think it would be quite possible for a flange joint assembly to be field-assembled sufficiently tight to withstand a low pressure leak test (say 35% design pressure, per PCC-2), but not tight enough to necessarily be leak-tight at full design pressure. At design pressure, internal pressure could load insufficiently preloaded flange bolts and unload the gasket, leading to leakage.
3. If design pressure is intended to be a credible pressure-temperature combination with the process fluid, then there should not be any fear of taking the system to this operating point with an inert test gas.
As mentioned, I have searched reasonably extensively, but cannot find any code or standard to support this view. Furthermore, the ASME codes seem to hold to the view that low-pressure sensitive leak tests are adequate proof of joint leak-tightness.
What is the general consensus and practical experience of field installation of prefabricated piping spools?





RE: Field Pressure/Leak Testing of Shop-Hydro'd Piping Systems
http://virtualpipeline.spaces.msn.com
"What gets us into trouble is not what we don't know, its what we know for sure" - Mark Twain
RE: Field Pressure/Leak Testing of Shop-Hydro'd Piping Systems
The leak test could be accomplished with water, with pressure monitoring and visual inspection to ensure integrity. Be careful about drying the piping out though, especially if it will carry high temp process. You can also perform a pneumatic test as you mentioned, and use snoop or soapy water for visual inspection at each joint.
RE: Field Pressure/Leak Testing of Shop-Hydro'd Piping Systems
I have form the Line List that the Testing Pressure (air) is 12 bar for Instrument Air & Utility Air.
What to do?
Do I have to propose something else? Which kind of test (hydrotest or leak test? The plant it's under Offshore regulation.
Another question.
Is it true that the demineralized water for Stainless Steel testing if stored in a Carbon Steel tank can be "contamined" and not used?
Thanks for your help