fluoride design water well
We are designing plans for a Water Well.
The City wants to add a Fluoride room and I've never designed a Fluoride room.
But I have seen a Fluoride room for a similar Well.
There were 2 storage tanks, a mixer, control panel, and pumps.
Does anyone have any advice on what products to select (like a Chemineer Mixer), what types of sizing requirements I will need to know, any additional items I may need??
Any additional advice will be appreciated.
Thanks.
RE: fluoride design water well
Don't recommend fluoridation but if you have to put it in, here are some guidelines.
Note: Make sure that you put in automatic shutoffs as fluoride is extremely poisonous and people have died because the fluoride feed equipment continued to run after the water was shutoff.
The godfather of fluoridation is/was Tom Reeves, he wrote this manual:
http://www.cdc.gov/MMWR/PDF/rr/rr4413.pdf
You can also check with the state where you live. Here is a typical guideline from a state:
SUBPART G: FLUORIDATION
Section 653.701 Fluoridation - Engineering Design Criteria
a) Procedure for Submitting Plans and Specifications - Design documents for fluoridation shall be prepared and submitted in accordance with 35 Ill. Adm. Code 602.
b) Basis of Design - Equipment shall have the capacity to maintain the fluoride content in the finished water between 0.9 and 1.2 mg/l.
c) Selection of Chemical - Fluoride compounds shall meet requirements of Section 653.202 and the AWWA Standards.
d) Chemical Feed Equipment - Feeders shall be accessible for repair and maintenance, protected against dust hazard and be accessible to the chemical storage area.
1) Weighing scales for measuring the daily amount of chemicals shall be provided for dry feeders.
2) Scales or a volumetric device shall be provided for determining the amount of solution fed.
3) Dust collection equipment and ventilation shall be provided where loading operations may create dust hazards.
4) Corrosion-resistant containers with non-corrodible covers and over-hanging edges shall be provided for solution feeders. Openings shall be constructed to prevent contamination.
5) A free chlorine residual of 10 mg/l shall be maintained in solutions prepared from dry chemicals. This chlorine residual shall not replace the chlorination requirement of 35 Ill. Adm. Code 604.401.
6) Chlorine shall not be added to hydrofluosilicic acid solutions.
7) Corrosion-resistant parts shall be used in the pump headers when hydrofluosilicic acid is fed.
e) Point of Application - The point of fluoride application shall be selected to provide uniform fluoride concentrations in the distribution system. Fluoride solutions shall not be applied ahead of ion exchange or lime softening processes.
f) Operating Controls - Controls which eliminate any possible hazard of over-dosing shall be provided and operate feed equipment only when there is flow past the point of application. Automatic stop-start operation and proportional feeding shall be used. Separate equipment installations shall be used where fluoridation at a single point is not possible.
g) Back-Siphonage Safeguards - Anti-siphon devices shall be provided for all make-up and dilution water lines and on the discharge side of the chemical feeder. An air gap or a siphon breaker in compliance with Section 653.801(d) on the downstream side of the last control valve in the water supply line serving the feeder shall be provided.
h) Auxiliary Treatment - Water used for preparing batch solutions or used for dry feeders shall be softened or stabilized with polyphosphates if precipitation of fluoride compounds interfere with the accuracy of the fluoride feeding equipment.
i) Safety Items - Rubber gloves and a dust mask shall be provided with each installation using dry chemicals. Rubber gloves, acid-resistant aprons and protective goggles shall be provided where hydrofluosilicic acid solutions are fed.
j) Metering - Facilities shall be provided for metering the dilution water and the plant discharge to the distribution system.
k) Testing Equipment - Testing equipment for fluoride ion concentration determination shall be provided and shall be:
1) a colorimetric comparator, or
2) a specific ion electrode with expanded scale pH meter.
l) Sampling Taps - Sampling taps shall be provided and located such that representative samples can be obtained from:
1) the raw water line before fluoride solution is added, and
2) after fluoride solution is added and has thoroughly mixed with the water being fluoridated.
Section 653.702 Fluoridation Treatment Equipment Start-up
a) Operating personnel shall be provided instructions for the use of the fluoridation equipment.
b) An Operating Permit shall be obtained prior to initiating operation of the fluoridation equipment. The Illinois Department of Public Health shall be notified as soon as fluoridation has been started.
Section 653.703 Fluoride Sampling
a) Samples shall be submitted monthly to the Illinois Environmental Protection Agency laboratory.
b) Sample containers will be furnished by the Illinois Environmental Protection Agency.
Section 653.704 Fluoride Operating Records
a) A copy of the daily operating report record signed by the certified operator or registered person in responsible charge shall be submitted to the Illinois Environmental Protection Agency each month as required by 35 Ill. Adm. Code 606.101. These operating reports shall show:
1) amount of water pumped;
2) fluoride chemical used;
3)
4) amount of fluoride chemical fed
5) gallons of dilution water used;
6) calculated fluoride dosage; and
7) fluoride ion test results.
b) An individual set of records shall be maintained for each installation when more than one source of water with separate fluoridation equipment is used.
c) A copy of the daily operating report records shall be maintained by the official custodian of the community water supply.