Balancing Multiple Digester Gas Flows

Balancing Multiple Digester Gas Flows

Balancing Multiple Digester Gas Flows

(OP)
I'm looking for information regarding methods for balancing biogas flows from multiple anaerobic digesters.  The digesters have balloon type covers and develop ~10" wc.  A few of the digesters are located further away from the common collection point and will need to have a low pressure blower to get the gas to the collection point at sufficient pressure.  

Is it as simple as piping them all together at the common header and engineering the header pressures within 2" of each other?  Are there any issues with installing PRVs to ensure that this happens?

Any insight/practical experience on this is greatly appreciated.

RE: Balancing Multiple Digester Gas Flows


You will have to check with suppliers of relevant equipment and experience with this type of gas and pressures.

One item is although, as you mention, the pressure balancing arrangement for the complete installation.

I will recommend a single running pipeline from each separate collecting point/ballon to burner tank, and with a check valve near inlet end, to prevent backlash or fire spreading from headstock /burner tank.

To getting the system working properly: keeping sufficent pressure at burner side, and controlled inlet into burner tank, I think you will eiter have to ensure that pressure difference between the different sections is large enough at any time to prevent trouble, or you will have to supply control instruments and controlled opening  and closing of motorized valves to shut off and supply from one pipeline at time.


 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources