apartment attic protection

apartment attic protection

apartment attic protection

(OP)
Comapny is psrinkling an apartment attic and using qucik response heads in the attic.

good bad allowed or not

reference if not allowed

thanks

RE: apartment attic protection

Attics are light hazard occupancies.  See list in Appendix A.5.2

A.5.2  Light hazard occupancies include occupancies having uses and conditions similar to the following:

<snip>

Unused attics

For sprinklers used in light hazard occupancies see section 8.3.3.1(1) below.

8.3.3 Thermal Sensitivity.
8.3.3.1*  Sprinklers in light hazard occupancies shall be one of the following:
(1) Quick-response type as defined in  3.6.2.9
(2) Residential sprinklers in accordance with the requirements of  8.4.5
(3) Standard response sprinklers used for modifications or additions to existing light hazard systems equipped with standard response sprinklers
(4) Standard response sprinklers used where individual standard response sprinklers are replaced in existing light hazard systems
8.3.3.2  Where quick-response sprinklers are installed, all sprinklers within a compartment shall be of the quick-response type.
8.3.3.3  Where circumstances require the use of other than ordinary temperature–rated sprinklers, standard response sprinklers shall be permitted to be used.
8.3.3.4  When existing light hazard systems are converted to use quick-response or residential sprinklers, all sprinklers in a compartmented space shall be changed.

 

RE: apartment attic protection

Opps, hit the enter key by mistake.

In answer to your question quick response sprinklers are required in attics unless they meet one of the listed exceptions which is rare.

RE: apartment attic protection

(OP)
thanks I just wanted to make sure

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources