Short Circuit Contributors
I am interested to ask whether we should include Frequency converters, harmonic filters and capacitors as contributors and model them in calculating short circuit currents.
I was having an impression that motors connected to VFDs do not contribute that much and are negligible, same as capacitors and harmonic filters.
RE: Short Circuit Contributors
Regenerative drives can contribute to external faults, the others can be ignored.  Capacitors actually can contribute some current, but are universally ignored for a variety of reasons.
Hi dpc, if it is not too much to ask, may I ask the variety of reasons why capacitors may be ignored (to educate myself further)?
Hi Nightfox. Mabey this will help. Consider the natural response decay of a discharging capacitor. Now plug some realistic values in for R and C. You will have an extremely fast decay which makes the initial condition insignificant. Hope this helps.
BOb
Normally the power factor of fault current is very low - the current is highly lagging.  Whatever capacitor fault current that occurs will be about 180 degrees out of phase with the inductive current.  Also, the capacitor fault decays very quickly - normally within a cycle.
There is a lengthy discussion of capacitor fault currents in Conrad St. Pierre's book "A Practical Guide to Short Circuit Calculations."
But I don't think ANSI or IEC standards for short circuit calcs have any guidance regarding capacitors.
Motors on non-regenerative drives can be ignored only if there is not a bypass contactor.  Regenerative drives will contribute some but not as high a magnitude as a motor directly on the line.
Thank you very much for all your inputs. I will order the St. Pierrie Book.
Thanks Rags004 for the R-L-C circuit recap.
Thank you for the reminding me also about the bypass contactors...I am learning a lot from this forum.
Hi nightfox1925,
As a supplier of complete installations comprising converters and harmonic filters, I've been working on Isc calculation on marine HV networks. My conclusions are :
1. For converters:
Only converters with thyristor bridges on network side (ie static frequency converters) can contribute to a short-circuit. They will contribute only if the short-circuit occurs when the drive is regenerating. You can find quite good explanations in IEC61363-1. Calculations are quite difficult as the contribution depends on the operating point of the machine at the time the fault occurs;
2. For harmonic filters and capacitor banks:
Obviously they are never taken into account. Our calculations on a few typical projects have shown that due to the time constants of these R-L-C circuits, they do not contribute to the peak value of the short-circuit current, wich is usually the most critical value to verify.
Hope we are in phase guys?