Why non magnetic material for cable armour

Why non magnetic material for cable armour

Why non magnetic material for cable armour

(OP)
Our specs say the cable armour shall be of a non-magnetic material. A supplier has proposed using galvanized steel. My company has asked the supplier to replace the galvanized steel with Alumınıum. Sınce the supplier ıs sourcing the 1x630sqmm 33kV cables from an experienced manufacturer,I believe the use of the proposed galvanized steel is a normal practice.
1) Why should the armour be of a non-magnetic material   
2) What is the advantage of Alumınium over steel?

RE: Why non magnetic material for cable armour

(OP)
Since I`m yet to receive a reponse to my post, I will be pleased if someone can gıve me a link to a previous post on the cable armouring. Thanks

RE: Why non magnetic material for cable armour

Running a single phase within a magnetic conduit causes undue heating of the conduit.  If all three phases are run within the conduit and loads are balanced, then the heating is minimized.

 

RE: Why non magnetic material for cable armour

Steel armor will be much heavier than aluminum armor.

RE: Why non magnetic material for cable armour

If this is a single-phase cable, magnetic conduit is not an option as mentioned by MikeDB.  The steel will quickly get hot due to magnetic field flux exciting a current in the steel.   This will generally cause cable insulation failure due to heat.

But I find it hard to believe that a cable manufacturer would even propose such a construction.  If it is three-phase, it comes down to cost, weight, durability, etc.   

RE: Why non magnetic material for cable armour

In addition to the advices give above by MikeDb and dpc, I would also suggest you to look at the glands and the gland plated on which the cabled will be terminated.
If you are using single phase cable, then the cable glands and the gland plate shall be of non-ferrous material (usually brass or aluminium), to cancel the magnetic field that will induce currents which will produce heat, and so on...
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources