55 sq ft bathrooms .

55 sq ft bathrooms .

55 sq ft bathrooms .

(OP)
Do I have to include the shower unit in to the room sq footage ?   or just the actual floor area ?  I have bathrooms in a university dorm that have a total sq ft of 56 sq ft including the the shower area . I remember someone stating that you don't have to include the shower at seminar i was attending a few years ago , but I can't find anything to back it up .   thanks !  

RE: 55 sq ft bathrooms .


nfpa 13 2002 edition


8.14.8 Dwelling Units.
8.14.8.1 Bathrooms.
8.14.8.1.1  Unless sprinklers are required by  8.14.8.1.2 or  8.14.8.1.3, sprinklers shall not be required in bathrooms that are located within dwelling units, that do not exceed 55 ft2 (5.1 m2) in area, and that have walls and ceilings of noncombustible or limited-combustible materials with a 15-minute thermal barrier rating including the walls and ceilings behind fixtures.

RE: 55 sq ft bathrooms .

From what I remember, the shower exclusion was often applied incorrectly.  So, in the 2002 version, possibly 99, the wording about excluding the shower was removed.  So now, you always include it.  You also need to have that 15 minute thermal barrier behind the fixtures.

Travis Mack
MFP Design, LLC
 

RE: 55 sq ft bathrooms .

(OP)
Thanks Travis ,

I did comfirm ,  it was the 2002 version when they changed
the code .  

RE: 55 sq ft bathrooms .

Don't know where you are located, but the ahj here does not require the showers/baths as square footage if there is a bathroom that is that close to >55 sq. ft. I guess it depends on what version of nfpa they are using. It would probably be beneficials to talk with your ahj first before throwing heads in all bathrooms. In 2007 edition nfpa 13d 8.6.5, there might be an argument there as to why you don't have to include baths/shower areas. hope this helps

tony

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources