Is there any data on sizing the lightning arrestors used on voltage regulators, normally connected source to load?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Voltage Regulator Lightning Arrestors
|
RE: Voltage Regulator Lightning Arrestors
Keith Cress
kcress - http://www.flaminsystems.com
RE: Voltage Regulator Lightning Arrestors
If you had a 7200 V regulator, the series winding would normally see 720 V at most (i.e., 10%), so a low voltage arrester of 750 V or more would work.
You'd still have a 9 or 10 kV arrester at the terminals, but you'd also have one for the series winding.