Deflections under Seismic Load Effects
With regards to the seismic load combinations utilizing the overstrength factor (ASCE7-05 section 12.4.3), I am trying to find guidance on appropriate deflection limits. I suppose there are two classifications of response, 1) Code referenced and 2) Sound Engineering judgement.
1) I'm not finding any code reference aside from those in Table 1604.3 of the 2006IBC and they specifically mention wind, nothing about E.
2) Earthquakes are expected to cause damage, the extent of what is tolerable is left to the judgment of the engineer...
I wonder if there were a few opinion on this subject?
RE: Deflections under Seismic Load Effects
You must determine your elastic story drift from your primary analysis and then apply the Deflection Amplification Factor, Cd, found in table 12.2-1. This per section 12.8.6, and 12.12.
Your sketch shows a discontinuous lateral system which, in my engineering judgment, warrant standard beam deflection limits (Table 1604.3) on the support beams (i.e. the rim beam AND the cantilevered beams at the ends) subject to omega level seismic forces combined appropriately with dead and live loads. If the deflection limits are exceeded, I would recommend using larger beam sizes.
Be sure to check the requirements for those if they do apply.