braided flex connector failure
braided flex connector failure
(OP)
I recently had a flex connector fail on the radiator piping for a large generator. It has been speculated that the flex connector was installed at a angle great enough to cause turbulent flow and increase pressure dramiatically.
Does any one know if there is a straight pipe distance down stream of a connector required to avoid this situation?
Does this hypothesis make sense?
Does any one know if there is a straight pipe distance down stream of a connector required to avoid this situation?
Does this hypothesis make sense?





RE: braided flex connector failure
For any type of hose, there are limits for offsets & min-radius. If the installation radius is too tight, you will reduce the hose cross-section and this can result in greater dP for a given flow. Ensure you have not exceeded the hose capabilities by the nature of the installation.
Was this a corrugated SS hose with SS braid? If so, look at the application guide from the manufacturer and ensure that the maximum offset was not exceeded. Contrary to some folks beliefs this type of connection cannot handle much offset. I have seen these specified by engineers with the belief that no thermal expansion calculations are required when they are used because the flexible metal hose will “take care of it.” They are often wrong. Ensure the hose installation does not exceed the manufactures’ installation limits, both hot and cold.