×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Vapor Barrier for Flat Roof

Vapor Barrier for Flat Roof

Vapor Barrier for Flat Roof

(OP)
Where can I find the calculation to determine if a vapor barrier is required for a flat roof?  What reference?

RE: Vapor Barrier for Flat Roof

I think generally a vapor barrier is always required on the "warm" side of an insulated wall or ceiling to avoid condensation whenever the dew point temperature falls  somewhere in the wall cavity.  In some climates the warm side can be either the interior or exterior, also  depending on season

15 or so years ago Here in massachusetts it was popular amongs dry-wallers to omit VBs in the ceiling, supposedly to aid in avoiding over-humidifing the living space in winter.
I put 6 MIL poly in our ceiling below the insulation anyhow.  With dogs, cats and kids the doors are open so often that we get plenty/too many air changes   

RE: Vapor Barrier for Flat Roof

(OP)
The problem we face is that on the 3rd and 4th floors of a 4 story building (the bottom two floors are open parking deck), condensation is forming on air grills located in the drop ceiling.  This only occurs on days that are over 100 degree F.  The design temp is 96 Degrees F.  We are trying to determine what is causing excess moisture and/or heat to find its way into the space above the drop ceiling.  We are using a systematic approach and making a list of possible items which may cause this to occur.  One is the absence of a roof vapor barrier.  If we calculate that one is needed, then the absence of one could be a contributing factor...if the roof does not need it per the calculation, then we ignore that item.  Project is in South Carolina.

RE: Vapor Barrier for Flat Roof

There is a good practical article on roof design in the latest ASHRAE journal.

However, I doubt that the roof would be causing a uniform problem on the 3rd and 4th floor though.  Basic physics check - Is the supply air temperature (i.e. grille temp) less than the dewpoint of your space.  Is your space temp and humidity within spec?  Is your AHU/RTU doing as it should?  Has someone recently umm...messed with it?

Is outside air leaking in and condensing on the grilles?  If this is happening closer to the perimeter or near doors this would be my first check.

Is there water being carried over from your coil - face velocity?   If the coil is not adequately dehumidifying the air, you have another contribution to the problem.  Is the moisture limited to the face of the grilles, or all through the ductwork?


 



 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources