Hydrogen Piping
3
Hydrogen Piping
Hydrogen Piping
I am looking for info on hydrogen piping design.  I know there are some different design considerations than there are for natural gas, crude, etc.  If any one has any info please let me know.
RE: Hydrogen Piping
What are the design and operating conditions for your hydrogen piping?  What is the hydrogen partial pressure for your service?  Depending on the temperature and hydrogen partial pressure you may not be able to use regular carbon steel materials.  Check out API-941 (www.api.org), Steels for Hydrogen Service at Elevated Temperatures and Pressures in Petroleum Refineries and Petrochemical Plants, for the so-called "Nelson" curves.  This document will provide much guidance for material selection for hydrogen service.
RE: Hydrogen Piping
Hello !
We have just completed re installing a portion of H2 line in our Plant. The Piping material is carbon steel and the valves istalled are very high valve leak proof Tech. Becareful, when we tested the line using water, It was ok. However when we run Nitrogen test , it was leak every where. The valves need special maintenance to repair. If you need more information I can provide u with it. The line which we installed was 40 Kg/cm2 Presure and ambiant temperture.
RE: Hydrogen Piping
Thanks for the help.  Sharq, what grade pipe was used?  I am researching criteria for a Hydrogen Pipeline.  Right now it is not known what the operating conditions will be.  I just want to have a good idea of what I need to specify when I go out for quotes on material.  Again thanks for the help.
RE: Hydrogen Piping
Hello again,
The material is A53 Gr.B. I have to bring to your attention to the following requirement when ordering
1- Chemical cleaning is required after pipe fabrication if hydrogen is used in a sensitive process reaction. (If you want the procedure I can givre it to u later)
2- Testing of the line must be by air / Nitrogen !
3- The valve specification for this line is very important. If you want I can provide you with manufacturer name.
4- our operatin pressure as I have mentioned is 40 kg/cm2 , hence a 100% radiography is required for all welding (Tig weld) joints.
5- Be carefull of instrument / Analyzer sample points, it should be fitted perfect.
6- Good luck :)
SHARQ (samir)