Dam design calculations
Dam design calculations
(OP)
I've been tasked with designing an oil spill containment. The best design is to build a concrete wall, approx. a foot high, perpendicular to an asphalted slope of about 1:10. My PE says he threw out all of the old concrete design books, and no other references are available or authorized for purchase. I want some calculations (or a free on-line reference) so I can show myself that the wall will hold water, resist a bump from a truck, and not overturn, slide or sink. I will submit it all to my PE for his approval once I am done.
I have not had any luck finding my old school books and notes. Any help will be appreciated.
I have not had any luck finding my old school books and notes. Any help will be appreciated.





RE: Dam design calculations
Is this crude oil, then maybe an asphalt surface is OK. I would have thought you would need either concrete or a geomembrane.
Can't help on the structural design, but based on typical concrete dimensions I've seen you probably only need 6" thick concrete, but it should be reinforced and include contraction joints at intervals.
RE: Dam design calculations
RE: Dam design calculations
h
RE: Dam design calculations
http://en.wikipedia.org/wiki/Bunding
If you make the wall sufficiently broad (broader than it is high) than it should not tip over. Reinforcement would be primarily for crack control.
RE: Dam design calculations
RE: Dam design calculations
civilperson- Thank you. I have a PE certify all of my containments upon installation and every ten years.
bridgebuster- I did check some USACE manuals on line. Thank you very much for the link. I was able to find some more useful information from the link.
cvg- Thanks for the information and saving me from over-engineering this task.
RE: Dam design calculations
The usual design is a reinforced concrete wall around the tank with enough volume to contain 110% of the tank and the local jurisdiction usually approves this.
The design uses an 8" thick concrete wall, 3' high, 10" slab, and 18" footing, reinforced w/ say #4 rebar @ 12" o.c..
http://www.pdhonline.org/courses/s131/s131.htm
The asphalt is probably ok if you are not going to have any spillage during normal operations, just secondary containment. The design has to be able to hold the spill vollume long enough such that cleanup operations can be completed.
RE: Dam design calculations
http://dat