Dear All,
Sorry if this question has been posted before, I have found 2 thread about E/F protection on D-Y transformer, but not cover my question below.
1. We have experience Hi-Z fault on LV(400V) O/H line which is supplied by 11/0.4kV Delta-Star with solid grounded pole XFMR around 50kVA. At the secondary side of XFMR we have cut-out fuse and can not available to provide Hi-Z protection. Could anyone give me the best solution for this situation ? (see attached file)
2. We would like to trip the 11kV breaker in substation which 1500 mtr away from the pole XFMR as illustrated above. Should I use radio relay or fiber optic converter?
3. What data should I provide to calculate the protection device for above case?
Thank you in advance and if you need some calrification please contact me. Sorry for my english.
Regards,
Eskim
Sorry if this question has been posted before, I have found 2 thread about E/F protection on D-Y transformer, but not cover my question below.
1. We have experience Hi-Z fault on LV(400V) O/H line which is supplied by 11/0.4kV Delta-Star with solid grounded pole XFMR around 50kVA. At the secondary side of XFMR we have cut-out fuse and can not available to provide Hi-Z protection. Could anyone give me the best solution for this situation ? (see attached file)
2. We would like to trip the 11kV breaker in substation which 1500 mtr away from the pole XFMR as illustrated above. Should I use radio relay or fiber optic converter?
3. What data should I provide to calculate the protection device for above case?
Thank you in advance and if you need some calrification please contact me. Sorry for my english.
Regards,
Eskim






RE: Hi-Z on LV Overhead Line
RE: Hi-Z on LV Overhead Line
volt secondary and hang the transformers there. No secondary involved. If the primary goes down it should trip the sub breaker.
RE: Hi-Z on LV Overhead Line
The best indication we have on our low voltage system is when the customer realises that he has lost 3 phase supply, or a single phase customer rings up without supply.
There are low voltage fault location units around that look for intermittent faults on underground cables. They basically sit there putting a time domain reflectometry pulse on the line and constantly calculate what the line "looks like" from a reflectometry point of view. When the line changes - either a phase to earth fault or open circuit or phase to phase fault - the unit will trigger some signal to the user (either hardwired or mobile phone sms) so that you can do something about it. The unit may work on overhead lines, but may not have as great a sensitivity as on underground cables. Might be worth a try. - try the Kelman Rezap Fault Master.
Phil
RE: Hi-Z on LV Overhead Line
Only two possibility detect this type of fault: or NPS current or NPS voltage protection on the end of 400V line.
NPS voltage is better, becouse NPS current detect also single phase load.
BTW, we had thread on the topic.
NPS voltage will detect all type of faults, include same type of fault ( broken conductor) on the 11kV side .
In case of broken conductor you can send trip to the 400V CB only ( if you have of course).
Regards.
Slava
RE: Hi-Z on LV Overhead Line
"BTW, we had thread on the topic."
What is the topic subject title..?
Can I use 59G relay with input comes from broken delta PT tapped from 400V line directly?
Eskim
RE: Hi-Z on LV Overhead Line
NPS is negative phase seq or at ANSI code 46 function.
Yes, against fault as describe in your OP, you can use 59G.
you can use simple undervoltage relay 27.
Intresting discussion was at the attached thread
thread238-201894: blown fuse detection
Regards.
Slava