Guys,
I have a question for anyone with UL expertise. I am modifying a IEC based switchboard design to pass UL891 here in the States. The IEC design allows multiple Mini-Circuit Breakers (UL 1077 "supplementary protective devices") to be tapped downstream of our incoming Utlity/Genset breakers (4000A, 100kAIC). This is a "no-no" for UL (dang product liability laws in the US!).... ABB does make UL 489 ("branch circuit protective") Mini-Circuit breakers, but they are only rated at 10kAIC. Does the fact that these MCBs are UL 489 branch circuit rated all us connect via a bus tap even though the bus is rated 100kAIC? The obvious solution is to use fuses, but our UPS system MUST know the status of the breaker/fuse. They do not make fuse blocks with "blown-fuse" auxiliaries that I know of...Anyone have any thoughts, suggestions??
As always, any help is greatly appreciated.
Colin
I have a question for anyone with UL expertise. I am modifying a IEC based switchboard design to pass UL891 here in the States. The IEC design allows multiple Mini-Circuit Breakers (UL 1077 "supplementary protective devices") to be tapped downstream of our incoming Utlity/Genset breakers (4000A, 100kAIC). This is a "no-no" for UL (dang product liability laws in the US!).... ABB does make UL 489 ("branch circuit protective") Mini-Circuit breakers, but they are only rated at 10kAIC. Does the fact that these MCBs are UL 489 branch circuit rated all us connect via a bus tap even though the bus is rated 100kAIC? The obvious solution is to use fuses, but our UPS system MUST know the status of the breaker/fuse. They do not make fuse blocks with "blown-fuse" auxiliaries that I know of...Anyone have any thoughts, suggestions??
As always, any help is greatly appreciated.
Colin





RE: UL891 - Mini Ciruit Breakers
Of course this means that the two breakers will not coordinate at high levels of fault current.
Are these smaller breakers in the same enclosure as the 4000 A breaker? If not, conductor sizing must meet NEC.
BTW, I believe there are fuse holders that will provide microswitch contact output based on fuse status. You might check with Bussmann.
RE: UL891 - Mini Ciruit Breakers
If you really need 100kAIC, fuses are probably your only option and like dpc also said, there are BFI (Blown Fuse Indicator) fuses out there that have spring driven pins in them which activate a microswitch in the fuseholder.
RE: UL891 - Mini Ciruit Breakers
http:
And by the way, you are going to have to know the voltage at which you want that 100kAIC, it makes a big difference.
RE: UL891 - Mini Ciruit Breakers
I doubt there is actually 100kAIC available, but certainly b/w 65&100kAIC, and I think UL 891 makes you rate the switchboard at the lowest kA rating of any device upstream of a PT (i.e. branch circuit protectors). Like you say, I don't think putting these in series MCCBs is very practical. Howerver, DPC led me to call Bussman, and they do have something that will work great. A new "CCP" line of fuse holders that have aux contacts for blown fuse indication (specifically for a PLC like this application)
http://www.cooperbussmann.com/2/CCP.html
Initially I called Ferraz-Shawmut directly, and the representative told me they couldn't make the "microswitch" device like you mention to pass UL specs, and that they were currently "arguing" with UL and hope to have it pass soon. I wasn't holding my breath for UL to make any sudden changes, though........ Maybe the guys was "BSing" me, but it looks like Bussman has something that works, so great!!
Thanks,
Colin