Induction motor with Drives

Induction motor with Drives

Induction motor with Drives

(OP)
Hello!

When starting a induction motor with drives, one usually start at low frequency and get high output torque, and the inrush current is reduced dramatically compared to DOL start. Can someone explain why the inrush current is reduced?

Thanks

RE: Induction motor with Drives

Slip is reduced.

RE: Induction motor with Drives

davidbeach is correct - but a bit short - in his answer.

The high starting current (equal to locked rotor current) when starting DOL is because slip is 100 percent and then gradually decreases down to nominal slip (or lower if motor not fully loaded) as the motor gets up in speed.

When using a VFD, the motor is kept at or just above nominal slip during the whole start. Frequency is increased, usually linearly, at a pace that keeps torque and thus current low.  

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Induction motor with Drives

(OP)
Thanks for the answers!

If the load requires a start torque 2 times the nominal, how does the drives manage to produce that torque when the current is limited? I stuck up in the where the torque is proportional with the power dissipation in the rotor.

 

RE: Induction motor with Drives

It can not. Not if the current limit is below current needed to produce double rated torque. You will need to set the limit higher - or use a larger drive.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Induction motor with Drives

(OP)
Ok, now Im beginning to understand:)

What is the maximum typical current limit (X*FLC) that a drive can have. If a DOL requires 6*FLC to produce a torque 2 times nominal torque, what will the current limit be with a drive?   

RE: Induction motor with Drives

It can be a lot less, actually. It is because the DOL start is very "torque inefficient". You do the starting way down the speed/torque curve and get very littel lb-ft per ampere. Using a VFD can reduce the current needed a lot. It also depends on the motor characteristic. A NEMA "A" motor will need perhaps 2.2 - 2.5 FLA to deliver 2 times rated torque. You can only do this for a short time, like during start up.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Induction motor with Drives

(OP)

Hello Gunnar.

Thanks for the answer. I understand the difference know :)

"Takker så mye for hjelpen!"

 

RE: Induction motor with Drives

So, where in Norway (or Denmark, perhaps) are you? I am in Karlskoga.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Induction motor with Drives

(OP)

I'm from Norway and live in Oslo. I work as a consultant actually. I used to work for ABB, mainly with switchgears and high voltage physics. Electrical motors isn't my strongest subject, but it is fun to learn something new!

RE: Induction motor with Drives

We are going there to have some kveite soon. Only place you get a decent one. Swedes overcook it.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Induction motor with Drives

(OP)
Kveite is very good and tasty fish, but I more fan of salmon fish. Anyways you can try gravlaks or lutefisk, typical Norwegian food ;)

RE: Induction motor with Drives

..or rakörret..

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Induction motor with Drives

(OP)
Thanks again Gunar for your help!

Maybe I have more questions in the future!

Thans and take care!

RE: Induction motor with Drives

To further add to the answer, most motors started DOL will not produce 2x rated torque until they reach >70% speed. Typically, they produce a low of about 120% torque and a high of about 240% torque as they accelerate.

On a VFD, you are always running on the part of the motor curve between the breakdown torque speed (the torque peak) and the synchronous speed (100% motor speed). Looking at the curve, you can see how it is possible to create more torque than a full-voltage type of start since you can use that torque peak at any rpm with a VFD.

If you look at the curve and find the motor torque you want then read the motor current off the curve to find how much current you need. You need a VFD capable of producing this current if you want the torque.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources