Hi to all.

I am presently involved in a project where lot of RTD's (Resistance Thermal Devices) are installed on field equipment, particularly on transformers and electrical motors windings.
As I am preparing the Cable List for the whole field, is there any specific requirement for the cables that will be connected to these RTD's, or I can simply use a normal copper couple? Is there a requirement for screening the couple/cable?

Thanks for suggestions.

Kind regards to all.

Giuseppe

RE: RTD cables

Hi Giuseppe,

Copper wires will be fine, please do twisted pairs to minimize differential noise.  Sensors with substantial impedance (like an RTD, typically 100 or 1000 ohms) can make an effective antenna out of your loop wires, so it's best in most cases to use shielded cable.  Ground the shield drain only on one end, though -- to prevent current due to ground potential differences.

As for conductor size, you can get really small if needed.  RTD transmitters typically don't put more than 10 microamps thru the loop.  If your runs are long, though, consider a third or fourth wire so that you can negate the wiring resistance.

Good on ya,

Goober Dave

RE: RTD cables

Most industrial RTD circuits use a screened 3-wire (triad) cable. The third core is used in a poor man's version of a Kelvin connection, using only one sense wire. The elctronics compensates for 2x the volt-drop measured by the sense wire. For precision work a four wire true Kelvin connection is used.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: RTD cables

ScottyUK is right, you must use 3 wires (triad) otherwise you will get significant errors due to different cable lengths or temperature change.
Be aware also that you may have more than one type of RTD. It's quite common for motors to use 10 Ohm Copper instead of the usual 100 Ohm Pt.
Different curves are possible also 0.0385 or 0.0392 Ohm/Ohm/°C

Roy

RE: RTD cables

(OP)
Hi to all.

thanks for the useful information. I will see how better use them then.

Great to know that you are out there, indeed...

Best regards to all.

Giuseppe

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources