Kinetix 6000 Overvoltage fault
Kinetix 6000 Overvoltage fault
(OP)
Hello,
I have a Allen Bradley Kinetix 6000 Servo controller connected to a Compact Logix PLC using a SERCOS communication network.
My problem is the Kinetix 6000 controller is faulting on overvoltage. I can see the overvoltage fault when in the Motion Groups folder online, but haven't found the actual dc bus voltage. Any help in where or if the dc bus voltage can be monitored online?
Thanks
I have a Allen Bradley Kinetix 6000 Servo controller connected to a Compact Logix PLC using a SERCOS communication network.
My problem is the Kinetix 6000 controller is faulting on overvoltage. I can see the overvoltage fault when in the Motion Groups folder online, but haven't found the actual dc bus voltage. Any help in where or if the dc bus voltage can be monitored online?
Thanks





RE: Kinetix 6000 Overvoltage fault
This information should be stored in the controller tags which is located in the Controller {file name} folder. Look for the axis that is faulted (which you've determined using the Motion Folders Group) and there should be a property called {axis name}.DCBusVoltage.