Parallel Emergency Loads
Parallel Emergency Loads
(OP)
Please consider the following:
1. Existing E/G system is a random access, parallel, three E/G switchgear.
2. A 3000AF drawout power breaker on E/G switchgear is presently serving a 480Vac, 1200A load using 4/phase 600MCM Al conductors. The linear distance is approx. 1000ft.
3. A new 3000A, 3 phase, 4W Cu busduct feeder was installed to replace the Al conductor feeder.
4. A last minute decision was made to retain the exisiting Al feeder fed from the 3000AF breaker and conncect the Cu busduct to the same breaker using 600MCM Cu conductor. To do this 6 new Al/Cu lugs/phase will be added to the breaker output. Each feeder will be serving separate loads. The power breaker rating plug will be increased to 3000A.
Some of us feel that the busduct feeder should utilize a separate breaker. This will provide an opportunity for better coordination, diversity, selectivity, etc.
Opinions please.
1. Existing E/G system is a random access, parallel, three E/G switchgear.
2. A 3000AF drawout power breaker on E/G switchgear is presently serving a 480Vac, 1200A load using 4/phase 600MCM Al conductors. The linear distance is approx. 1000ft.
3. A new 3000A, 3 phase, 4W Cu busduct feeder was installed to replace the Al conductor feeder.
4. A last minute decision was made to retain the exisiting Al feeder fed from the 3000AF breaker and conncect the Cu busduct to the same breaker using 600MCM Cu conductor. To do this 6 new Al/Cu lugs/phase will be added to the breaker output. Each feeder will be serving separate loads. The power breaker rating plug will be increased to 3000A.
Some of us feel that the busduct feeder should utilize a separate breaker. This will provide an opportunity for better coordination, diversity, selectivity, etc.
Opinions please.






RE: Parallel Emergency Loads
Just too many issues and I would simply distance myself from such installations or design. If you are a junior engineer working with bunch of "experienced" people who come up with such clap-trap ideas, sooner you leave them better would be the prospect of your future career!
1. What is a random access E/G system? (not that it matters here).
2. It appears that 3000A busduct was installed replace the 1200A feeder so it is going to the same general destination as the 1200A feeder. Most you can get out is 3000A so what good does the 1200A feeds do?
I hate to give free professinal advice to such "designers" but here it is: Why not install a distributio board with at end of the new 3000A busduct and install a 1200A brach breaker in that distribution board to feed the 1200A load?. Reuse the part of the original 1200A condcutors as necessary to save money.
3. The arramgement you describe would be considered a Tap of the feeder. Refer to tap rules in the NEC article 240, and none of which apply here. Most that can be inferred is the tap must end in its own set of fuses or a breaker.
4. Are you upgrading the 1200A feed itself to 3000A by adding more conductors? (Dont ask me why on earth you would do that) You cannot protect a 1200A feed by a 3000A breaker.
RE: Parallel Emergency Loads
Initially, the 3000AF had a 1200AT plug to comply with NEC and protect the 1200A Al Feeder. This feeder services a dedicated load of HVAC equipment (smoke mode control exhaust fans, elevators, central station lighting).
A 3000A busduct was installed and will feed a separate dedicate load of similar equipment and systems.
The total load on the E/G system will be within its continous and starting load ratings.
The decision to re-plug (3000AT) the 3000AF power circuit breaker and feed both the 1200A feeder and the 3000A busduct was made by management to save money.
Some of us are trying to convince management that a separate appropriately sized breaker must be used to allow us to provide the proper, coordinated, protection.
Concerning your comment, it is the other way around, the folks trying to convince management to use a separate breaker are experienced graduate engineers (I am the only one with a PE though); the group that has convinced management to use the same breaker are relatively young electricians with electrical construction and installation experience under their belts.
RE: Parallel Emergency Loads
RE: Parallel Emergency Loads
Well now you have some more ammunition. At the least put your opinion in writing to the "management".
Wish you well.
RE: Parallel Emergency Loads
Does this installation have to be inspected?
I would estimate the cost of doing this installation plus the cost of changing it when the AHJ rejects it and compare that to the cost of doing it right in the first place in my submission to management.
Consider your liability as the only PE around if there is an issue and people are looking for someone to blame.
Bill
--------------------
"Why not the best?"
Jimmy Carter