Hi everybody,

Our client has asked if we can install a smoke evacuation system in the building that they are going to occupy but the building ownder does not agree since it is not specified in the local fire code. Do you have any references in the NFPA, ASHRAE or any standards that can show that these are requirement? Thank you in advance for your responses.

Mechathan

Mechathan

RE: smoke Evacuation System

It all depends on building size...  IBC (I think section 909 or 910) has requirements for smoke exhaust systems, IMC (Section 513) has specifics on design.

If you don't fall under the requirements of the code (which wouldn't be surprising) the insurance company (loss prevention) of the business could require it, but that would be your only other way to "force" the owner to install a system.

I don't think you want to get into installing smoke control in an existing building.  Sealing the barriers between control zones may be impossible with the building occupied.  If the zone barriers aren't sealed, the system won't segregate areas properly.  Then you spent all that money for nothing.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources