NEC clearance with cable tray

NEC clearance with cable tray

(OP)
Does anyone know what the NEC clearance has to be from a cable tray containing #8's for power and an energized piece of equipment (A/C condenser & pump within metal enclosure)?  Currently the tray is about 4' above the condenser.

RE: NEC clearance with cable tray

Don't think the NEC cares at all about this.  The tray could run right down to the equipment.  

RE: NEC clearance with cable tray

Hi swartzmech
I agree with dpc the NEC doesn't care about the minimum height above the floor.
But as mentioned in 318-3 b only solid bottom trays will be permitted if "conditions of maintenance and supervision [does not] assure that only qualified person [that means electricians] will service the installed cable tray system". I think that in an industrial zone as mentioned above only rigid conduits[well grounded] are recommended to drop up to an equipment from the cable tray[my opinion!].
Best Regards

RE: NEC clearance with cable tray

I think a cable tray manufacturer would know the ends and outs of these specs.

I used this manufacturer

http://www.cablofil.com/


Cable tray installation guidelines
NEMA Standards Publication VE 2-2001
see attached file


This was a freebee from the manu website on Nema standards.  NEC just has guidelines.

It seemed like the standards we used was driven by the manu and customer and the local supplier's guidelines on installation.

 

RE: NEC clearance with cable tray

(OP)
Thanks very much dpc, 7anoter4, and controlsdude.  BTW, all of my tray exits will be RGS.   

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources