Designing a Combination Section

Designing a Combination Section

Designing a Combination Section

(OP)
I am designing a S12x40.8 beam that needs a C10x20 placed on top to form a combination section.  I would like to show a stitch weld to attach the two sections together.  How do I calculate the size and length of the weld to assure the combination section will act as a single beam? I have looked in several books and can not find any answer

RE: Designing a Combination Section

what sort of loads are being transferred across the welds ? ... shear, bending, axial ... i could guess but why ? ...

RE: Designing a Combination Section

(OP)
The beam has a trolly on the lower flange carrying 5.5 tons.  

RE: Designing a Combination Section

Check shear flow at the interface, f = VQ/I.
I guess this is a motor driven trolley, in such case, I will use bolted connection rather than weld.

RE: Designing a Combination Section

(OP)
The contractor wants the connection to be welded.  This beam is being added in the field in a tight spot.  I was just uncertain how to design the weld to make a combination section or "Built Up" Section.

RE: Designing a Combination Section

calc the shear flow as mentioned above and size the welds accordingly.  Try a stitch weld 3"@12" - with the interface being near the top of the section, the shear flow is likely to be small.

RE: Designing a Combination Section

Wuth the number of holes that would have to be drilled to a 2.75" gage, field welding would be the better option even considering the uphand weld condition.  

And, yes, VQ/Ib is your equation of choice to find the shear flow.  You will not find any tables in AISC publications for this type of connection, although you will find combination section tables.  The 9th edition has your specific combination on page 1-83, but you have to calculate the interstitial shear for the connection and design it yourself.

Mike McCann
MMC Engineering

RE: Designing a Combination Section

(OP)
When I go to calculate Q do I use the area of the Channel and the Area of the flange at the connection?  Or do I use the area of my combined section?It has been along time since I did Mech of Material.  

RE: Designing a Combination Section

(OP)
I believe I figured it out
thank you

RE: Designing a Combination Section

Check the fatigue. Stitch welds performed poorly under repeative loading/high stresses reversal, and vibratory environments. You will find bore holes on site is not that difficult and unusual, provides there is adequate space to lay the beam on ground. On the other hand, the quality of field welds is quite of a concern.

RE: Designing a Combination Section

I second kslee1000's last comment.  Use a continuous weld.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources