Please have a look at the attachment. The Red circle shows the three phase connection of Isolated phase bus bar to the generator .The rated voltage of the generator is 21kv, Which means the Um value is 24kv, from IEC the clearance is 220mm, if choose a lightning impulse voltage of 125kV.

Say i choose to have a clearance of 220mm in the red circle area and a higher clearance value say 270mm in the blue circle area.
What are the weak points in the above configuration.Is there any disavantage in having such configuration, with different clearance along the Isolated phase busbars.
What are  the problems associated with testing of such configurations?
Please suggest.

RE: High Voltage CLEARANCE

It would be pretty difficult to design an installation where all clearances equal the minimum allowable.  If there is a surge that exceeds the 125 kV withstand, the flashover will occur in the red area, not the blue area.  Except for an impulse flashover test, there should be no effect on testing.

RE: High Voltage CLEARANCE

(OP)
Thank u for the reply.
I have a clearance of 125kV in the area near the generator and clearance of 145kv away from generator.

Now if i have a surge, higher than 125 kV then it would strike the area near the generator, this is pretty clear.

 However say if i have a clearance of 125kV through out, that is near the generator and far away from the generator, then wat would happen if the configuration faces a surge more than 125kV?

RE: High Voltage CLEARANCE

Quote:

However say if i have a clearance of 125kV through out, that is near the generator and far away from the generator, then wat would happen if the configuration faces a surge more than 125kV?
Then you would not be able to predict where the flashover would occur.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources