Mineapolis bridge - yes again
RE: Mineapolis bridge - yes again
Interesting.
I know nothing about bridge design but it seems to me that the wording of this report is slanted toward the assumption that the original design was flawed.
However, it also states that a concrete deck was added and a central concrete divider.
Thus:
Quote:
NTSB Chairman Mark Rosenker didn't comment on the photos, but has said the original design for the bridge specified steel for those and other gusset plates that was too thin.
This appears to judge that the original design was wrong and that the concrete deck was not a factor.
So how was the concrete decking and divider not a factor?
AM I wrong in thinking that adding the concrete should have required a design review that should have either exposed the original design flaws or shown that the design was not such as to support the added loads. In other words, whether the original design was right or wrong, wouldn't there have been a design review necessary to permit adding the concrete and wasn't this flawed whatever else comes to light?
Or, is it possible that the concrete addition design review simply looked to see if the added load was within the original loading allowances? In which case it would suggest that the review did not go back to first principles but assmed the original calculations or design were sound.
JMW
www.ViscoAnalyser.com
JMW, you are quite correct in your questions and comments.  I'm sure this will haunt someone (somebodies) for quite some time.
1.  Original design appears to be flawed but bridge stood for 40 yrs.
2.  At some point plates bend, bridge stands for years.
3.  Addtional weight was added but bridge stood for years
4.  Contractor makes modifications and adds construction materials to bridge, bridge stands for weeks, months.
5.  When contractor redecked the bridge the first time what did they do differently?
I don't mean to imply it was the contractor but just suggesting that the bridge has seen it's share of loads and renovation in the past.  Something must have been different.
Qshake
pipe
Eng-Tips Forums:Real Solutions for Real Problems Really Quick.
It is very easy to look at the calculations and say hey these were 2% under therefore that must be the cause, but it is much harder to actually find the cause from other sources.
Lawyers are not interested in the truth, only potential liability. They will take the easiest path to compensation for their clients.
I attended a conference in West Virginia not long ago where a federal government engineer with a substantial reputation in the structural engineering community explained what he learned in the investigation.  Gusset plates connecting the two ends of a diagonal member were undersized.  As memory serves, he computed the needed thickness as 1 and 3/8ths inch.  The plan detail showed 3/8ths inch thick.  The original plan detail was off by a factor between 3 and 4, which is consistent with bridge design factors of safety typically used.  The construction loading did contribute to the failure he believed, but was on the order of 115-130% of the original design, not 300-400%.  After the fact, folks are looking at inspection photos where a bit of a bend may be observed in some gussets.  Unfortunately, I wouldn't expect an inspector to proclaim that as an indication of imminent failure.  How is he to know it wasn't bent slightly in the shop or during erection?  It just goes to show all the effort we put into quality control, whether it is during the plan development process or during construction or somewhere in-between, is all for a good purpose.
Dinorsaur -
I'm afraid if those were the numbers for the actual plate size, then you've been mis-informed.  Similarly with the correct size of the plates.
It's amazing how much mis-information there is and how willing engineers are to spread it.
While I don't disagree that an inspector should observe a bent plate as a sign of imminent diaster, it should have been dealt with more promptly.
That this is true is to remember the I-90 Cuyahoga River Bridge in Cleveland which underwent an extensive retrofit for gusset plate stiffening.
I think this all shows that we, as engineers, need to do more to get our lessons learned out to the community of engineers and owners as well as our achievements.
Qshake
pipe
I'm not a bridge engineer, but I did take basic drafting and know a "true view" when I see one.
Such is not the case of the two diagonal photos on the site.  Taken two days apart, neither photo confirms in my mind that the gussets were bent.  That could only be confirmed in an end view photo of the gusset.  Unless they have more definitive photos in their hip pocket here, I would contend they are not bent.  I believe what you are seeing is just a corner of the gusset at the intersection of two cut faces.
And the lawyer's comments, typical BS...
Mike McCann
MMC Engineering
Qshake,
I'll speak to him and write the values down when next we speak.  Could you check your notes and see if you can find the actual values also?
Dinosaur - First, please keep in mind that my statement was not a personal attack...not that you took it that way but I wanted to be clear.
From the material on the website at MnDOT for the original plans, they list the gusset plate thickness as 1/2".  The interim report by FHWA (available on the internet) which focused on the U10 and L11 plates determined that the plates were about 1/2 their proper size.  In that report I reference you to Table 4.  Earlier in that report you will see a table of D/C ratios wherein, a 2.07 for shear is indicated for the U10 plate.  This is where the conclusion that the plate is half the necessary size.
I hope this helps to clear up a few things.  And I hope, for the sake of you presenter's reputation, that he was misunderstood.  Otherwise, he was misinformed and is spreading mis-information.
Qshake
pipe
"Gusset Stiffening"
Yak, snort, etc.
- Steve
Mike - The plans on are on the MnDOT website as are the shop drawings.  The only cut line for the plates that are not vertical are the lines normal to the diagonals and those are basically the width of the diagonal.  Hence there really is no other oblique planes for the plates.
I'm not really trying to convince you of the likelihood of a bent plate, but rather trying to lead you to information that may help support or refute your claim.
Qshake
pipe
so, if they decided the gusset plates were too thin, when were they planning to change them or did they only find out after the bridge failed?
JMW
Thanks Qshake - I'll check it out.
Mike McCann
MMC Engineering
jmw - since I am a bridge engineer, I have followed this matter.  It's my understanding that the plates were not found to be thin until after the collapse.
Qshake
pipe
Qshake:
Could not find the drawings on the website, so I'll have to take your word for it.  Too many drawings to go through!
I'm curious about the structural design theory here though with the utility of the gusset plates.  As I see it, the only way they could buckle is if they were resisting a moment at the joint and buckled due to overloading, whether it was gravity induced or cylical.
Sounds to me like these joints were not designed as pinned, but moment resisting - possibly partial moment resisting.  What is the design spec on the gusset plates that drives the thickness requirement?  Minimum moment capacity, bolt/rivet bearing, brittle fracture... what?
Thoughts?
Mike McCann
MMC Engineering
Mike, All those items need to be checked including shear for different planes and for block shear failure.
On the matter of designed as moment resistant, I doubt that in 1965, all truss bridges were designed with member stiffnesses accounted for.  I think the joint was designed as pinned and through the typical details of the connection, it winds up being a moment resistant connection.  In other words, I think that the joint itself is very stiff, in plane, versus the members.  Out of plane is a different story and when edges aren't stiffened may be prone to buckling.  Either laboratory testing or lessons learned were part of the development for the AASHTO plate edge stiffening.
Qshake
pipe
Thanks Qshake,
But I see the photos purporting to show distortion are from and intact bridge.
The question is if these photos induced concern at the time they were taken, in which case that should have been the time they started to check the calculations and plan remedial work, or these photos were only examined after the event.
If they were only examined after the event why did they not create concern at the time?
What else was photographed and why?
JMW
So many questions, so few answers. Best to wait until the investigations and court cases have run their course.
Qshake:
OK, I can accept that.  My only other concern though is that if the gussets provided joint rigidity that was not designed for then the following happens:
1.  The members are seeing forces less than what was designed for and have KL/r values less than the original design due to joint fixity.
2.  The joints are seeing moments for which they were not designed.
3.  If the joints were designed as pins, the lack of stiffness of a failed gusset should not contribute to the bridge failure as it would be merely another level of energy absorption that was not included in the original design adding to the overall safety factor.  In effect, the gussets would be springs that were overloaded.  A further redundancy for the system.
Item 2, to me, is the critical one here, but there are undoubtedly others.
Just thinking out loud here.  And, yes csd, we will have to wait, but it's still fun to guess. bigsmile
Mike McCann
MMC Engineering
Mike - I don't disagree with your points but will note that:
1.  Not necessarily a bad thing, eh?
2.  Since the gusset plates are being designed for (by AASHTO specs), the average of the actual stress and member strength but no less than 75% of the member strength, and since both criteria are independent of the actual load caeses since same load case may not elicit maximum stress in all members framing into gusset, it is likely that the gusset was designed to resist quite a force above what it should.
3.  Failing the gusset is not good due to it's relatively weak out of plane behavior.  Addiitonally any large displacements in the gusset from failure will negatively impact the truss by changing the geometry and load paths.  This loss of stability can collapse the bridge.
Qshake
pipe
I was at TRB when a bit of a report was given by FHWA and one of the consultants who worked on the investigation.  The gussets were 1/2" when similar gussets elsewhere in the bridge were 1", which is what got people looking at their design to begin with.
Because the original design calcs are gone, there is no way to know if it was a design error or a drafting error.  The investigator said because of the particular distribution of the construction loads, that node in the bridge was seeing the highest load it had ever been under before.  That's what was different.
Everything was a factor; if the bridge hadn't been redone over the years with more concrete barriers and more traffic, the undersized gussets might have survived (then again, maybe not, considering the particulars of the construction load distribution), but if the gussets hadn't been undersized, all the concrete barriers, increased traffic, and construction loads would have been fine.
Hg
Eng-Tips policies:  FAQ731-376: Eng-Tips.com Forum Policies
HgTX -  I'm not sure I agree with your last statement "if the gussets hadn't been undersized, all the concrete barriers, increased traffic, and construction loads would have been fine."
Those or other gussets may be overloaded as more load is added and no analysis done to show what is the capacity.
It is normal procedure for us and our clients to submit calcualtions showing that for additions such as bulk materials and batch plants etc will not overstress a structure.  If anything this horrific failure has shown us that procedure isn't adhered to as it should be.
Qshake
pipe
I find it hard to imagine a bridge, subject to the lane loading live load of 300 psf, failing due to the imposition of construction loading.  Obviously there was no traffic in the area of the construction....???
If the committee is pointing there as the reason for the failure, as I gather from the posts above, I don't think they have looked far enough.  It just doesn't add up to me.
Mike McCann
MMC Engineering
They were saying it was the particular pattern of where the construction materials & equipment were placed on the bridge.  A concentrated load here, an absence of load there, etc.
Either that or it was a big conspiracy.
Qshake:  "if the gussets hadn't been undersized, all the concrete barriers, increased traffic, and construction loads would have been fine."  An earlier version of that sentence, before I posted, included something about analyses for increased load that assumed the connections were stronger than the members framing into them--which they weren't, because of the undersized gussets.
Hg
But HgTX, the AASHTO code only requries gusset plate connections to be designed for the average of the actual stress (or factored loads) and member design strength but not less than 75% of the member (deisgn) strength....hence connections are not designed over and above members which the NTSB chairman has stated.
As such, gusset plates, like all structural elements should be checked and not ruled out just because engineers believe them to be stronger than any other elements....
I hope I'm not missing your point.
Qshake
pipe
Where did the live load value of 300 psf come from?  Not 550 plf/lane?
Even with the 75% rather than 100% requirement, there's still an assumption that can be made about the connection without directly analyzing it.  IF one knows which code the connection was designed to...IF the connection was designed correctly...
I'm not sure what my point is.  I think it's that analyses were probably done for the various load increases using assumptions reasonable at the time.  The collapse shows that those assumptions aren't reliable.
Hg
I'm not particularly mnechanically oriented and haven't followed the discsussion.  Just looked at the link and have an observation and a question.
Observation:  Photo's 1 and 2 have different date stamps... 2 days apart.  Seems like someone saw something unusual and went back for another look?
Question: What's a gusset and where is the supposed bent gusset in those photos?
electricpete - Those are two different joints that are photographed, one on 6/10 and the other on 6/12.
For a symmetrical truss, that is symmetrical about centerline of mid span and centerline of structure, there should be 4 joints that are nearly identical except for location.  for that joint in question, it is U10.  U10 has four duplicate locations.  For example, U10W, U10E and U10'W and U10'E.  W and E designate the west and east trusses and in this case, the prime (') and non-prime represent the nort and south locations about centerline of mid span.  clear as mud?!
Qshake
pipe
Actually, I'm with Electricpete (not just in knowing nowt about bridges) in not really seeing what these photos are supposed to show.
Qshake, for us ignoramuses, is it the plates on the sides of the joints that connect across from one structural member to another?
Are these the sort of view an engineer would take or a tourist? Perhaps to the trained eye the problem is obvious but I'd have thought a view that is exactly end on would be better to show the warping to better advantage.
JMW
Photo 1 and 2 shows a clear kink in the vertical edge of the  gusset plates. That would make them useless in compression.
the gusset plate is the thin vertical squarish plate reinfrcing the joint between the main members.
Although the kink looks small, it would be enough to destroy the stiffness of the plate.
Cheers
Greg Locock
SIG:Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
Greg - I differ from you stance on the matter of the kink and it's effect on the plate.
Because of the location of the kink, I believe it reduces the capacity of the plate to transfer signicant and maybe even the design compressive load but I believe that if the buckle or deformation where at the end of the member framing in, then it would indeed zero out the plate as a means of load transfer and any transfer after buckling would be left to binding between members.  But the deformation at the edge away from the fastener pattern where the load is being developed from member to plate is likely to continue to have some capacity.
JMW - The gusset plates are those that sandwich the members (verticals, diagonals and horizontals ) together.
Qshake
pipe
I think that's what I thought.
JMW
civilperson:
Sorry that I pulled the rabbit out of the hat here...  I got the300 psf value from an old 1963 California Bridge Design manual we used in school.  This "lane loading" controlled in short span situations where the H20 and others controlled in longer spans.
Mike McCann
MMC Engineering
lane load is 640 plf plus a concentrated load of 18k for moment and 24k for shear