grounding of 12 pulse transformer

grounding of 12 pulse transformer

grounding of 12 pulse transformer

(OP)
i start to design project  with 1600hp,069kV motor driven by 12 pulse VSD,the supplying transformer to VSD shall be 12 pulse transformer 22/o.69/o.69kV DYn11 Dd0, do i need to ground the Y seconary, and how the VSD monitor ground leakage in the trafo secondary.   

RE: grounding of 12 pulse transformer

Take a close look into the drives manual. Not grounding the incoming supply will expose some parts ot the drive (driver circuits, current sensing)to higher voltage stress, at least when there is an unintended ground connection elsewhere.

RE: grounding of 12 pulse transformer

I guess you will have a problem grounding the Delta secondary. Unless you corner ground it - which I wouldn't recommend.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: grounding of 12 pulse transformer

Go by what the drive manufacturer requires.  A ground reference in the wrong place on a multi level converter can let lots of magic smoke escape.  A missing ground reference when one is needed can have similar effects.

RE: grounding of 12 pulse transformer

Grounding the starpoint on the Y winding will also provide a sound reference for the rest of the converter. The alternative would be no grounding at all (and -of course-isolation monitoring)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources