Fault level contribution by a generator.

Fault level contribution by a generator.

Fault level contribution by a generator.

(OP)
We have a gen set consisting of a 5oo MVA generator and a 0.415/11 kV Traffo. The generator has Xd'= 15.9 %, Xd''= 11.1 %. The Traffo has z = 4.58%. I have calculated the fault level but its too high.

May be there is something I have forgotten and please remind me which of the generator reactances is appropriate

Thank you guys in advance.

RE: Fault level contribution by a generator.

A 500MVA set directly connected to a 0.415/11kV transformer? Check your post and confirm the data you posted - something does not sound quite right.
 

----------------------------------
  
If we learn from our mistakes I'm getting a great education!

RE: Fault level contribution by a generator.

(OP)
Connection to the tarffo is via a circuit breaker

RE: Fault level contribution by a generator.

Still makes no sense.  A 500MVA Generator at .415kV??

RE: Fault level contribution by a generator.

Hi Punglu.
Maybe it's 500KVA!!! Please see again Scotty's post.
Regards.
Slava

RE: Fault level contribution by a generator.

(OP)
Oops sorrry for that, its 500kVA!!!

RE: Fault level contribution by a generator.

For calculate fault current, you should use Z"dv, so X"d = 11% in your case.  For this size of generator, you can take typical value of X/R of induction motor, approximately 15-20 for 500kVA

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources