Tranformer Circular Core vs. Rectangular Core

Tranformer Circular Core vs. Rectangular Core

Tranformer Circular Core vs. Rectangular Core

(OP)
I am looking for information on the advantages (and disadvantages) of Circular core transformers versus rectangular core.

I have heard that circular offers technical advantages but the rectangular core is cheaper. Can someone provide feedback on this?

The applications I am most interested in are
5MVA-20MVA @ 46kv/4.16kV
100-200MVA @ 230/46kV

Any literature would be helpful also.

Thank you

RE: Tranformer Circular Core vs. Rectangular Core

Talk with Waukesha - they will be happy to explain the advantages of the circular core.

The primary benefit is short-circuit  mechanical strength for through-faults.  Waukesha used to claim that they had never had a through-fault failure on one of their units.  

  

RE: Tranformer Circular Core vs. Rectangular Core

Well, there are other, very simple reasons:

For the same area (iron) the cirumference (copper, losses) for a circular core is less

Higher cost is due to more difficult manufacturing:
more different widths of iron, more care during stacking

But with raising cost for copper and energy no one should use rectangular cross sections for transformers above a few kVA

RE: Tranformer Circular Core vs. Rectangular Core

A good book on transformer engineering could help too as well as understanding different winding construction techniques for circular designs.  Of the transformers you listed the only one I'd consider for rectangular designs is the 5 MVA 46-4.16kV unit and that recommendation assumes that you have an on-line backup for the unit.  Anything larger or higher voltages requires, in my opinion, circular designs using disk or helically-constructed windings.

dpc, as for Waukesha's claim I've seen their mechanical through-fault failure first hand.........not any better than the rest in that regard although they've taken steps recently to improve their through fault mechanical performance.

RE: Tranformer Circular Core vs. Rectangular Core

I believe the only advantage of a rectangular core is the better use of physical space for vault considerations.

RE: Tranformer Circular Core vs. Rectangular Core

The short circuit concerns with rectangular coils are not much of a problem if the low voltage coils are full width sheet type.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources