"Loud Bang" heard during occupancy
"Loud Bang" heard during occupancy
(OP)
I was called to one a job today because a client heard a “loud bang” during occupancy of the building (which took place this weekend). This happened once on Thursday and again on Saturday in the same general area. During the site visit (which included a close inspection of the connections and suspended slab) I could see no sign of distress in the building. In talking to the people who heard the noise they said it sounded like someone “hit the steel with a hammer”.
Construction:
Bay 24’-0” by 28’-0”
Secondary beams W16x26 24’-0” long spaced 8’-0” o.c.
Girders W24x55 with 28 studs 28’-0” long
Slab construction
6” slab placed atop 2” 20 ga. Composite decking reinforced with 6x6 W2.1xW2.1 wwf.
The facility is a car dealership and they were basically moving cars around on the suspended floor when they heard the noise.
I have some theories on what it could possibly be but I am wondering if anyone has any ideas on what may have caused this noise.
Construction:
Bay 24’-0” by 28’-0”
Secondary beams W16x26 24’-0” long spaced 8’-0” o.c.
Girders W24x55 with 28 studs 28’-0” long
Slab construction
6” slab placed atop 2” 20 ga. Composite decking reinforced with 6x6 W2.1xW2.1 wwf.
The facility is a car dealership and they were basically moving cars around on the suspended floor when they heard the noise.
I have some theories on what it could possibly be but I am wondering if anyone has any ideas on what may have caused this noise.






RE: "Loud Bang" heard during occupancy
If you are a member of AISC, you can search their journal articles for "banging bolts" you can find a lot of research into this occurrence. I've read a little about it, seems kind of interesting.
It might not apply to your building, but it could be a start in the right direction.
Let us know what it is, if you ever find it.
Hope this helps.
RC
All that is necessary for the triumph of evil is that good men do nothing.
Edmund Burke
RE: "Loud Bang" heard during occupancy
RE: "Loud Bang" heard during occupancy
RE: "Loud Bang" heard during occupancy
What type of connections are they using for the gravity beams? Bearing or Slip Critical? Were the beam and the connection parts primed or masked off? What type of bolts (TC or regular) were used and were they partially of fully torqued?
RE: "Loud Bang" heard during occupancy
For the W16x26 they are using single sided angle connections. This was not my preferred connection but they worked for the light loads and made erection much easier.
The bolts are designed to be in bearing.
They applied 4 bolts per connection.
All connections are bolted – bolted.
The angles were attached to the girder in the shop.
I believe that the surface between the girder and the angle is unpainted. The surface between the secondary beam and the angle is painted.
I believed they used t.c. bolts that are fully torqued by evidence of shear spline removal.
As for the girder, they are double angle connections with 7 bolts in double shear (14 bolts to the column).
RE: "Loud Bang" heard during occupancy
RE: "Loud Bang" heard during occupancy
RE: "Loud Bang" heard during occupancy
RE: "Loud Bang" heard during occupancy